what happens if i connect acapacitor to a generator load
Answers were Sorted based on User's Feedback
Answer / loki
cap connected across the load improves operating pf
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / p k ajeshkumar
Connecting a capacitor across a generator always improves
powerfactor,but it will help depends up on the engine
capacity of the alternator,other wise the alternator will
be over loaded due to the extra watts consumed due to the
improvement on pf. Secondly, don't connect a capacitor
across an altenator while it is picking up or without any
other load.
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / b.ramesh
When capacitors connected across the DG load that there was
harmonics devoloped.That harmonics will be effect on DG
alternator and excitor to cause of winding failure.
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / phanendra babu
if we connect the capacitor across the alternator for
compensating the inductive load it will be more use full,
improves the p.f hence reduces the load on the Altrnatr. if
it is under no/light load condition,alternator output
voltage will increase more than the rated,hence connected
load will be effected and hissing noise will observe from
the alternator,hence it will effect the efficiency and life
of the alternator
Is This Answer Correct ? | 4 Yes | 6 No |
what is EBXl (electron beam cross linked ) cable ?
how encoder works?
what is the difference between equipment earth and system earth.
what is ph test in coolent cheking
What is domestic transformer? Draw the connection of domestic transformer.
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
What is mean demand of the Plant?
Why selected cable colour red yellow and blue in 3 phase Electrical system?
9 Answers Crompton Greaves, Essar, Gridco,
How much CTs are required to measure th curent in DOL starting of motor?PLs explain.
High speed earth switch operation with diagram
0 Answers KSEB, L&T, Sanden Vikas, Siemens,
where to use 3.5 core and 4 core cables, will this vary for type of loads
how speed control of induction motor?