Answer / carl_ellis
The problem is in the controller's PID tuning, which is
tuned to be too sluggish.
All of the loop's control components work properly:
- the transmitter reports the process variable
- the controller responds to an error (albeit too sluggishly)
- the control valve responds to the controller's output, as
evidenced by switching to manual mode
The PV response as reported by the transmitter depends on
the controller's appropriate response to error. If the
controller's response to error is sluggish, then the loop's
PV response will be sluggish.
Manual mode offers a means of overriding the PID's
calculated output value and driving the output to where it
needs to be.
This question qualifies as one of the best interview
questions I've read on this site. I'll be sure to use
this question when I interview candidates.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
Technician A says that a fuel tank sending unit will have a high resistance only when the tank is full. Technician B says that its resistance when the tank is full depends on whether the sending unit is designed for use with a bimetallic gauge or with a magnetic gauge. Who is correct?
I want to use 1/2 inch SS316 tube in my high pressure & temperature (64 kg/cm2 & 500 deg C)after condensate pot in pressure tranmistter. 1) Is it possible to use 1/2" ss316 tube in high pressure and temperature line. Tube manufacturer is local vendor. 2)On sarting the plant, We need to do system fluse that time condesate is not in the condesate pot so steam is directly contact with the tube. We have no exact calculation to know our tube is ok or nor at this time. pleae,reply.
please can anyone tell me in detail, what's mean by open loop and close loop?
If any control valve create hunting problem, what is the possible reason and solution?
What pressure transmitter.
What is ptw and write 3 types of ptw?
What is Span Error
What is passive connection of instrument in different types of IO module?
What is the formula To convert Degree centigrade to foranhight.
Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?
when an eddy current probe is installed inside of a turbine or compressor in case of probe problem same as:crash of head of probe,changing the scale factor because of low measuring gap(physical gap is ok(example=1.14mm)but voltage is reduced(example=-6 volts),is any way to check the probe,when the ohm of probe is ok.thank you,(Karim Tavakoli)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)