Answer / sabry
Actually It's called "Honed meter run".
It's a 1 piece manufacturer piping assembly, used to hold the orifice.
It's called "Honed" as the piping internal surface is honed/machined to be glass smooth surface.
This assembly is very expensive & it's used in custody transfer applications.
REFERNCE"Lessons In Industrial Instrumentation"/Page:584,585.
Good Luck
Ahmed Sabry
I&C Senior Engineer
Cell:+2 (0122) 1367310
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / inst & control eng
Honed flow sections are orifice runs made in sizes of 0.5"
to 1.5". These devices are used for low flows of gas,
liquids and steam services with a higher tolerance than
standard sized orifice flow measurement of pipe line size
more than 2".
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / murali
to create the differential pressure from that you cam
derive the flow of media
| Is This Answer Correct ? | 0 Yes | 4 No |
what is the difference between PLC & DCS
How you calibrate absolute pressure with the calibration range of 0 to 1000 0C Absolute. Please explain the procedure for calibration.
What is instrumentation amplifier?
what is IPS (instrument protective system)?
what is diff between the centrifugal and reciprocating
Why Instrumentation Air Compressor called as Instrumentation Air compressor?pls dont just tell its trasferring IA to all transmitter,valves.I need exact reason, please......................
hello i'am samad.Any one Can help me! How to calibrate Vaccum Transmitter DP Type range 0 - 50 mbar abs by hand pump calibrator.
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
How does a strain gauge measure pressure?
In control valve , Failure position : Close If it is Fail close(FC) during failure of AIR.. what will be the initial/ normal position of control valve is it normally open or close? please some one explain soon..
How to control flow variations in magnetic flow maters..... When i will provide proper earthing?
what is the calibration procedure for transweigh make weigh feeder?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)