Answer / carl_ellis
1) You can't calculate temperature from millivolts from a
thermocouple without cold junction compensation. The
thermocouple tables only apply when the reading is cold
junction compensated.
2) To determine temperature from a resistance value,
several data are required
- the type of RTD (Pt, nickel, copper)
- the temperature coefficient (the alpha) in Ohms/ohm/DegC
must be given - 0.00385? 0.00392?
- the RTD Standard, IEC, USDoD, DIN 43760 With the base and
the alpha tables are available on the web.
- the Ro, the nominal resistance at 0 deg C
The table you request is specific to the RTD in question.
No data, no table.
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 1 No |
What is the reason for not giving very High Proportional Gain Kp in PID Controller?
what happens when the profibus fails while in operation (operation of a valve)?
what is the zero and span trim?
If any control valve create hunting problem, what is the possible reason and solution?
In control valve proximity inductive sensor is taken as digital feedback for full open and full close.Normally its volts 24v when the sensor acts the feed back voltage 14v so that our relay not indicating in plc panel . kindly give the solution.
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .
Sir, I want junior executive, Instrumentation question papaer for IOCL, Plz send to arabinda.ghosh83@gmail.com
how to calculate density?
how do we commission inergen system?
give eg of how I/P is used in control loops
what is zero and span ?
why we use by pas on a positioner? When can a by pass be not used on a positioner ?