What is Loop Test & What is Loop Checking? Please i need
answer for these questions.
Answers were Sorted based on User's Feedback
Answer / kaushik4454
Friend,
Both loop test and checking are same in practically.
simulate 4 to 20 through hart/bt/hht. OR transmitter itself.Smart transmitter also have the facility to simulate ma.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raja
loop test mean hart communicator connect the transmitter
than simulate the MA 4MA to 20MA transmitter to DCS system
what are use for loop check
Loop verify the tag number transmitter to DCS system
verify the range the data sheet range transmitter to DCS system
| Is This Answer Correct ? | 2 Yes | 2 No |
Name some of the common protocol use in automation.
Describe all types and levels (4-20mA, 0-10V, mV, pulse, etc.)of analog and digital I/O used in process control application.
why we should maintain neutral earth voltage below 1V while calibration? why cant it be 1.2V or 2V
what is ZERO SUPPRESION and ZERO ELEVATION?
What is the difference between Error and Offset.
What are the charcterstics of a P&ID controller block for Governor speed raise or lower for a load sharing functionality between 4 Gas turbines in droop mode.
What is the purpose of LO Overhead tank in turbines.
what does it mean an active front end in vfd plz explain it briefly
A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.
Where should we terminate the shield and why?
square root calculation for dp flow transmitter? give me a explanation with example
What is the difference between fire detector and smoke detector?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)