T.x range -0.1 to 0.2 milibar,so how much mili ampear at 0.1 milibar?
Answers were Sorted based on User's Feedback
TX range is -0.1mbar to 0.2mbar
span= maximum-minimum
= 0.2-(-0.1)
= 0.3
mA = given value- zero value/ span x 16+4
= 0.1-(-0.1)/0.3 x 16+4
= 0.2/0.3 x 16+4
= 14.66 mA
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / sampath
LRV = -0.1 mbar
URV = 0.2 mbar
SPAN= 0.3 mbar
( 0.2/0.3 )* 16 + 4 = 14.67 mA @ 0.1 mbar
Is This Answer Correct ? | 11 Yes | 9 No |
Answer / dibyendu das
tx range= -0.1 to 0.2millibar
span =0.3
-0.1 = 4 mmA
-0.075 = 8 mmA
+0.05 = 12 mmA
+0.075 = 16 mmA
+0.2 = 20 mmA
this is the ratio to calculate 0.1 milibar = how much amps.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sarath kumar
tx range= -0.1 to 0.2millibar
span =0.3
hence, mA at 0.1 miilli bar = 9.28 mA
Is This Answer Correct ? | 4 Yes | 13 No |
what is absolute pressure and where use in process?
In field side transmitter voltage droping here no loose connection then what will happen?
difference between dcs & pld
how we can check level probe and controller
What is the use of gauge?
GWR radar transmitter working principle?
WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HIS message appears: Equalize start. HIS0163 WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. HIS0163 ---- ERROR = 3 WARNING = 1 ---- Tell me, please, why and how to solve the problem."
6 Answers Khas Pvt Ltd, Yokogawa,
whether radar level transmitter is applicable for the open tank
HOW FOREIGN CONTROL SYSTEM CAN BE CONNECTED WITH DCS?
How to check vortex flow meter is in good condition while we do not having calibration setup?
How works weighfeeders in cement industry? what is the working principle?
We are used ABB 800xa 5.1.please tell me how to instrall this.