Answer / carl_ellis
The Profibus DP specification defines the hardware transport
physical layer as 2 wire RS-485. The communications
protocol and the transport layer are both part of the
Profibus DP specification (the separate 2 wire cable for
24Vdc power supply is not involved with the communications).
Any device that passes Profibus DP certification will
conform to the Profibus DP specification.
Therefore, a 4 wire RS-485 device will not work on a
Profibus DP network because it won't be a Profibus DP
device, it does not meet the Profibus DP spec, which is 2
wire RS-485.
Attempting to operate a 4 wire RS-485 device on a Profibus
DP network will only disrupt Profibus DP communications on
the network.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 1 No |
How to convert m3/hr in tonnes/hr
why t/c is connected parallel and what is the purpose of it
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
I WANT TO KNOW SOME BASIC CONCEPTS RELATED TO INSTRUMENTATION
how to convert bar to mA?
What is the standard height for stancion supports?
Which standard of hazardous area classification used in India?
how u calibate pr tx without master tx?
what is control valve and how is work
I want condensate pots vent position erection of flow transmitter ?
what is exat meaning of compentation in RTD ? what diffrent between 2 wire,2 wire and 4 wire RTDs?
what is meant by nuclear collector?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)