Profibus DP is a multi-master system. Would it work on RS-485
4W or not, and justify your answer
Answer / carl_ellis
The Profibus DP specification defines the hardware transport
physical layer as 2 wire RS-485. The communications
protocol and the transport layer are both part of the
Profibus DP specification (the separate 2 wire cable for
24Vdc power supply is not involved with the communications).
Any device that passes Profibus DP certification will
conform to the Profibus DP specification.
Therefore, a 4 wire RS-485 device will not work on a
Profibus DP network because it won't be a Profibus DP
device, it does not meet the Profibus DP spec, which is 2
wire RS-485.
Attempting to operate a 4 wire RS-485 device on a Profibus
DP network will only disrupt Profibus DP communications on
the network.
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 1 No |
I want to take temp. data from recorder to computer. Which communication system is best from this option(Rs 232- 485/ethernet/USB)?
what is meant by Hydroelectric powerplant?
Describe the concept of Gain Scheduling, as currently found as an option in some controllers.
why micro controller 8051/52's clock frequency is internally divide by 12 ?? and why it is further divide by 32 in UART serial communication ??
I need the intools training institute address in india. Intools subject oriented local authors books.Refer me plz
can u briefly explain aboutan aryton shunt multirange DC ammeter?
In case of Transmitter's(e.g.Ultrasonic Flow meter ) we have an normal practise of selction of upstream and downstream distance such as (20D and 5D ).can anyone please let me know whow to calculate "D" ?? i guess it refers to pipe thickness is t right ?
What is the difference between fire detector and smoke detector?
why we use double acting valve and where?
What is the expansion of RADAR? How it works?
I have observed in field instrumentation work... I remove the fuse of an analog transmitter then it shows 7.75 kg/sq cm (which is practically wrong value)in DCS and when put the fuse it shows 0 in dcs. Then cheach the field transmitter termination and found moister. clean that and then it shows 1.1 kg/ sq cm which is right value. Please describe the above phenomenon.
How u will setup SPI(2007) on Citrix Server (Thin Client Mode)? Plz Justify?