what is the difference between single and double
compression cable gland
Answers were Sorted based on User's Feedback
Answer / r k nair
Normal Cable Gland is also called Single Compression Cable
Gland. As the name suggests, while you tighten the gland,
the grip or compression is effected only at one p[lace
(i.e.) at the cable armour only. There is scope for
moisture and corrosive vapour to enter the gland and thus
into the cable.
Whereas in Double-Compression Glnad, the compression
happens both at the cable armour as well as at the inner
sheath. This is sort of two sealings. Hence, chances of
moisture or vapour entry are minimised. Hence these glands
are also known as Weather-proof cable glands or Flame-proof
cable glands.
| Is This Answer Correct ? | 21 Yes | 1 No |
Answer / raffi
Single compression glands used for the unarmoured
cables.since you can make the grip only on cable sheath
whereas Double compression glands are used for armoured
cables as we can tight it with both cable inner sheath also
in cable armour.
Both glands can be used for exlosion proof areas, only
thing is that it should be certified for zone
classifications
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / sumith
single compression cable gland is used for normal panels and
it is not airtight.(it cant be used in flammable areas)
double compression cable gland is used for air tight panel i.e
purge panels(used in flammable areas)
| Is This Answer Correct ? | 2 Yes | 6 No |
How will you calibrate an Absolute Pr.Transmitter of range 400mmHg absolute ?
Distributed control system
how to calibrate transmitter
how to connect 3 wire 4-20 mA transmitter in Plc system PLC system and how explain how the measuring data communicate with plc system.
What is the procedure of calibration of Load cell?
I need to know steps to Calibration Valve Guard......
what is positive feedback and negative feedback?
Difference between ultrasonic flow meter and radar type flow meter
2 Answers Dodsal, Qatar Petroleums,
What is meant by cold float of compressor shaft.
in split range control valve,two valve should be in two different line and that should have some distance,and we have only one positioner feed back link.so how we connect one feed back in two control valves?if you have picture please forward me.my email id kb.syamkumar@gmail.com
1.can you use SCADA instead of DCS,DCS instead SCADA 2.Difference between DCS and PLC,can their role be reversed i.e. role interchange 3.Difference between RTU and PLC
0 Answers IOCL, Lakshmi Machine Works,
why we use cascade control and feed foreword control in 3 element control of boiler drum ?what is feed forward and cascade control system ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)