1,why we use 4-20 ma output of all instrument qhy not use 0-
20,
2,what is the different between PLC & DCS.
3,how can we meaure maximum span of new flowmeter if not
given any information.
Answers were Sorted based on User's Feedback
Answer / rohan g
0 to 20 vdc signal may detoriate over distance but current
signal will remain intact.
noise will not affect current signal at all but vdc signal
will get affected.
if equipment fails then also it gives 0 vdc signal in case
of 1 to 20 vdc.but not in case of 4 to 20 ma.
DCS can be viwed as bigger version of PLC.Since no i/p dcs
can support is more in case of dcs.Also dcs can have
operator interface but plc dosent have such.
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / narendra mishra
suppose 0 to 20ma is used where 0 for
min.process value and 20 for max.then if
feed back cable get shorten or erthed or
broken it wil show min process value.where
in case of 4 to 20ma it will show "bad".
Plc are used to handle specific area where
DI DO signals are required like burner
managment system.plc response time is in
milisec. And that of dcs is in microsec.
Max span can be found by taking it online
and interfacing it with HART.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / himanshu apte
4-20 mA current has the highest linearity with the field
instruments. Same linearity cannot be found in other
current options like 0-20mA or any others. In addition to
that, a cable failure in case of 0-20mA will not be
detected if the signal is already at 0 mA.
PLC have a very small scan time i.e. @ 50-100 milliseconds,
which is useful in Emergency shutdown systems..Controlling
algorithms are available in modern PLCs, but fine tuning of
controllers can be better achieved with DCS. DCS has a scan
time in the range @ 500ms, which is why it cannot be used
in ESD systems. DCS can also handle more no. of I/Os than
PLC.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / samir
4-20 ma is used to instrument because if there is an
instrument faulty of it not getting the power or damage then
it gives 0 ma signal so we can found that the instrument is
faulty so we can easily check the instrument.
if we use 0- 20 ma we can not identify from the signal that
the instruments is faulty or actual the low signal from the
instrument during the measurement.
| Is This Answer Correct ? | 0 Yes | 0 No |
how to do dynolab wind speed sensor loop test, how to simulate value,i have simulate mA 4-20mA but not responding in DCS faceplate, please kindly advice me any one.
How do you identify between actual alarm and false alarm in a Temperature Transmitter in SCADA based Control System
defination of radial vibration?
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
why micro controller 8051/52's clock frequency is internally divide by 12 ?? and why it is further divide by 32 in UART serial communication ??
What is cold junction compensation in thermocouples? How is it achieved?
Yokogawa mass flow meter shows negative reading...what r the main causes for this problem?...
How can i solve the problem of ROSEMOUNT 5300 guided wave level transmitter of full range? For more clearfication , another guided wave level transmitter VEGA brand have the same problem and i solved it by drain the champer from water and make "false signal suppretion" from transmitter push buttons it's configuration to tell the transmitter to avoid any built-up signal ,,, so my question how can i avoid the problem that rosemount read full range while the champer empty or any other ????
Can SmartPlant Instrumentation be used in a concurrent engineering environment?
Turbidity analyzer working principle ?
I am manjunath having exp in maintenance of chemical plants,know i want to do a design course INTOOLS,after doing design course can we get jobs in design field.sinve i dont have design exp..
WE Know that different supply voltage of solenoid valve like 24,110,220 etc..how we check the solenoid supply is 24v or 220 NOTE: No specification at device.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)