what happen if one of 3-phase line has a much higher load when
we are using delta to star transformer?
how we can over-come from that?
Answers were Sorted based on User's Feedback
Answer / sb
Upto certain extent it is allowable but beyond that O/C
relay may trip the circuit.
As said by the above friend abnormal neutral current will
flow & hence through the CT sec side & will actuate the relay.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / jigar bhanushali
Due to it system will be unbalance hence there will be some
neutral current .now if neutral of sta load is not grounded
then there will be harmonics ingection in the line which
will give poor performance of equipment used at load ide.
| Is This Answer Correct ? | 8 Yes | 4 No |
TYPE'S OF BREKAR ,WHAT IS TRANSFORMAR & SAFTY. STARTER DOL & STAR DELTA STARTER.
how to calculate
why power generate in 33 kv it will be step down by 11 kv .
How can you measure the signal from the PT100 sensor?
why is fan rotating slow speed, what is the problem?
How Calculat the Cable Sizing of HT/LT System & Explian by one Exampal?
how you configure motorvision relay (L&T make)from DCS
why induction motor takes high current?
What aturn on methods of scr?
how to calculate cable size in transformer, distribution side?
what is the safty of poly phase tranformer?
why CT ratio stand for 50/5, 100/5, 25/5.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)