Transformer and generators rating in KVA due to this is not
depended on power factor.Motors current depended on copper
losses and voltage depended on iron losses so, this is
depend on power factor.
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / swum
2 types of losses in transformer are
Ohmic loss which is dependent on current
core loss which is dependent on voltage
Since these 2 losses are independent of power factor, rating
is expressed in KVA instead of KW
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / g a reddy, essar steels ltd, v
The term power factor is related to load. It is not related to Generator and Transformer. I mean Power factor angle will not vary with out load.(cos of the angle between voltage and current.) This will vary depends on type of load.I can say capacitive loads will inject the reactive powers to line and inductive loads will draw reactive power(KVAR) from the line to develop a magnetic field in the windings.Active power is used to Drive the load(KW).
KVA= sqrt of(kw2+kvar2)
And also we can say Transformer and Generators Losses will depends on Voltage and current. So Ratings of these are mentioned in VA.
| Is This Answer Correct ? | 5 Yes | 1 No |
Actually Dg and Transformer Supplying Apparent power only . At the load point only power is segregated by real and reactive power.The Apparent power measured by the unit of kVA(Kilo Volt Ampere),the True power measured by the unit of KW,the reactive power measured by the unit of kVAR(Kilo volt ampere with reactive component).For that reason only DG and Transformer ratings are in KVA.
| Is This Answer Correct ? | 4 Yes | 3 No |
what do you mean by star point.its importance in ct & pt
what is MAR
Can you use a different size cable to complete a circuit if you run out what you are using?
if we connect a ohmmeter across shorted capacitor .what will be the reading..will it be zero or infinity
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same
what is meant by CT burden = 10 VA?
what are the sample questions asking to the test cunducting for electrical superwising lisence test?
how i chosse capacitor bank if my energy meter is 48 kvr? tell me capacitor bank chossen formula?
What is IDMT? What is the principle
1.Can anybody explain Why starters are not used for motor starting in industries? 2.
Could Please Explain briefly. Why used stabilizing resistance series with High impedance bus differential protection relay.
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)