In a running D.G set engine and Alternator is revolving at
1500RPM but no output in the terminal>>>>what to do??
someone told excitation problem ....please advice
Answers were Sorted based on User's Feedback
Answer / parvesh sharma
Some times the exciter will we discharge due to the leakage or reverse supply at this condition we excite the exciter of the alternator, from 24 volt DC external supply for few time than start the DG it will generate the full voltage.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sagar
There is AVR i.e Automatic Voltage Regulator in Alternator. You need to check its settings. There are two knobs provided V+ to increase voltage & V- to decrease voltage of alternator.
If after increasing V+ there is no change in voltage at alternator terminal then check excitaion system.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ashish
Unless a proper load is connected to the set, the system will not work.
Consider the load to be current and then check the output.
| Is This Answer Correct ? | 3 Yes | 3 No |
What happened when we give 2 phase supply to a 1 phase equimpent. It's effect on equipment's efficiency and life?
How to size fuse? How to size MCB?
How damper winding in synchronous motor suppress Hunting?
in the farm,water tank of 8000 litter capacity situated in 12 meter above.Farm owner want to lift 7000 litter of water within 7 minute to water tank of 12 meter above.which motor having HP rating is suitable for pumping??
1 Answers ABB, Anchor, Havells, Keltron, KSEB, L&T, vguard,
what is ten delta ?
What is the diference between increased saety motors and non sparking motors?
what is the difference between multimeter and megger?
what is the powerfactor
1.Whats the use of GNAC(Generator Neutral Accessory Compartment) 2. why generator or any other system require Neutral Grounding and not Phase grounding 3. what happens if any one of the phase is grounded. 4. if 15kv is grounded directly what will happen, why it should not be grounded like that 5. use of of NGTR(Neutral Grounding Transformer and Resistor) for grounding is helpfull and how
5 Answers BEMCO, CSS, Powergear,
how to change the load sharing between two synchronized identical alternators when both are running with Diesel engine? assume both are feeding to same feeder?
How can i check a relay good or not?
what is units of resistance
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)