In a running D.G set engine and Alternator is revolving at
1500RPM but no output in the terminal>>>>what to do??
someone told excitation problem ....please advice
Answers were Sorted based on User's Feedback
Answer / parvesh sharma
Some times the exciter will we discharge due to the leakage or reverse supply at this condition we excite the exciter of the alternator, from 24 volt DC external supply for few time than start the DG it will generate the full voltage.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sagar
There is AVR i.e Automatic Voltage Regulator in Alternator. You need to check its settings. There are two knobs provided V+ to increase voltage & V- to decrease voltage of alternator.
If after increasing V+ there is no change in voltage at alternator terminal then check excitaion system.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ashish
Unless a proper load is connected to the set, the system will not work.
Consider the load to be current and then check the output.
| Is This Answer Correct ? | 3 Yes | 3 No |
What is the IS standard for MCCB to be use (As per capacity of AMP)& for ACB also.
what is trip circuit supervision relay? How does it work in switchgear?
6 Answers Radha Regent Hotels,
What is an electric arc?
why do we use spark detector inside the slip ring brush compartment 0ona slip ring induction motor?
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.
HT/LT PANEL TEST?ALL TEST
There are 2 motors without name plate and terminal but one is DC motor and another is induction motor.How one can identify which one is DC and which one is AC motor?
why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage from 33kv to 415v directly using single transformer.
12 Answers ABB, Adani, Central Electricals, Electrical, HCL,
if neutral earthing is weak of a system then how can we improve it ? Technically explanation ??
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB to another Power DB?
How the over load setting for HT Motors calculated-provided in Numerical Relay
0 Answers Damodar Valley Corporation,
What is a soft start?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)