Answer / s pradhan
For 11 KV;Ph-Ph-130 mm
Ph-E -100 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
| Is This Answer Correct ? | 54 Yes | 19 No |
Answer / geetha
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
for 11 KV : Ph-Ph-229mm
Ph-E-178 mm
for 11 KV : Ph-Ph-229mm
Ph-E- 178mm
for 33 KV : Ph-Ph-320mm
Ph-E-320mm
for 132 KV : Ph-Ph-1100mm if Lightning impulse = 550
Ph-E- 1100mm
Ph-Ph-1300mm if Lightning impulse = 650
Ph-E- 1300mm
for 220 KV : Ph-Ph-1900mm if Lightning impulse = 950
Ph-E-1900 mm
Ph-Ph-2100mm if Lightning impulse = 1050
Ph-E-2100 mm
| Is This Answer Correct ? | 28 Yes | 10 No |
Answer / saleem
phase clearance between phase to phase and earth in
11Kv,33Kv and 66kv System.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / mathi
ans: 110mm for phase to earth
130mm for phase to phase
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / sinnadurai sripadmanaban
Please give clearances for indoor as well as for outdoor and in air/vacuum/SF6 or within a switchboard(enclosure-IP..)
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / bmw6633@gmail.com
phase to phase 1inch and for earth 1 1/2 inch
| Is This Answer Correct ? | 11 Yes | 25 No |
why write 500v on line tester (Test pen)
Induction generator has = A negative speed B negative slip C negative voltage D negative current
waht is the working principle of saft starter & what is the difference in vfd & saft starter
for high freq ac,why we first convert AC to DC and then DC to high freq.AC
when will cause the negative sequence falut in electrical system?
Which motor has high starting torque
what is infinite in infinite bus
why don't we use the generator as a motor? and what will happen?
why the transformer connected like STAR- STAR, DELTA- DELTA, STAR- DELTA, DELTA-STAR ...? why these connections ,,, explain the advantages these connections?
sir am giving jspl exam on 19th oct . i belong to eee, so plz send previous question papers ..........to dis id abhilash203@gmail.com
why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)
why do we need transformers?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)