phase clearance between phase to phase and earth
Answers were Sorted based on User's Feedback
Answer / s pradhan
For 11 KV;Ph-Ph-130 mm
Ph-E -100 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
| Is This Answer Correct ? | 54 Yes | 19 No |
Answer / geetha
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
for 11 KV : Ph-Ph-229mm
Ph-E-178 mm
for 11 KV : Ph-Ph-229mm
Ph-E- 178mm
for 33 KV : Ph-Ph-320mm
Ph-E-320mm
for 132 KV : Ph-Ph-1100mm if Lightning impulse = 550
Ph-E- 1100mm
Ph-Ph-1300mm if Lightning impulse = 650
Ph-E- 1300mm
for 220 KV : Ph-Ph-1900mm if Lightning impulse = 950
Ph-E-1900 mm
Ph-Ph-2100mm if Lightning impulse = 1050
Ph-E-2100 mm
| Is This Answer Correct ? | 28 Yes | 10 No |
Answer / saleem
phase clearance between phase to phase and earth in
11Kv,33Kv and 66kv System.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / mathi
ans: 110mm for phase to earth
130mm for phase to phase
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / sinnadurai sripadmanaban
Please give clearances for indoor as well as for outdoor and in air/vacuum/SF6 or within a switchboard(enclosure-IP..)
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / bmw6633@gmail.com
phase to phase 1inch and for earth 1 1/2 inch
| Is This Answer Correct ? | 11 Yes | 25 No |
what is the distance maintained between the power and data cables with respect to the KVA .... plss give me the formula
how to Select its CORE in electrical cables based on its applications? or Application of various types of electrical cable based on it CORE?
how many earthing should need for UPS, where its connected
WHAT IS OLTC OF TRANSFORMER? WHERE IS ITS USED EITHER ON PRIMARY OR SECONDARY SIDE OF TRANSFORMER?
what is the meaning of cable Glanding can you explain brifly?
how kva rating of transformer is calculated.
6 Answers Fluor Daniel, Siemens,
full form of flry b
Dear all, i completed M.E(Power Electronics & Drives) 2011 passed out having 78% so i need job in core side but i don't know how can i receive the calls from electrical companies and i uploaded my CV in naukri, times jobs etc.. In that iam not recieved any mails from good companies so give me best procedure plzzzzzzzzzzzzzzzzzzzzzzzz..... Thanks, K.Linga Reddy Email-id:-lingareddykmthm@gmail.com Ph no:-08015402078
for a 500 KVA connected load, I calculated 30% of capactor for power correction. Even after using 225 KVR capactor PF is not improving. What could be reason for low Phase correction factor?
Compare salient pole and cylindrical rotor machines.
how calculate busbar size for rated amps, which formula use
The principle of switching circuits for different types of batteries in application of storage systems
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)