For Synchronisation of DG Sets Sometimes we people use NIC
(Neutral Isolation Contactor) Instead of 4-pole ACB or any
switchgerar..Please guide me why is it so????
Answers were Sorted based on User's Feedback
Answer / srikanth shreenidhi
Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker
However when only one DG set is used we always go with 4
pole breaker.
Is This Answer Correct ? | 16 Yes | 8 No |
Answer / vinod
when a DG set is started and as dg voltage is building up it is necessary to connect the lowest potential point of generator first with the system which it is to be feed, that is the neutral as first. then the breaker can be closed if the set is required to be parallel first. the reason is the system which the DG is intended to supply may have a neutral potential which can be at a different potential other than the DG. so in order to establish a common neutral NIC is used. if NIC is not there and DG neutral is always solidly connected to the BUS then grounding impedance of the whole system is reduced and in turn fault in system can lead to a higher fault current.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / muniraja1283@rediffmail.com
above said subject full very satisfactury
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / zuber ahamed
Whenever DGs are paralled & synchronised one should have a
common neutral.If neutral of one generator fails
automatically the neutral of other dg sets which is on a
common bus takes over.Whereas if the DG has a 4 pole
breaker and neutral fails it will be impossible for the
system to continue as all the dg sets will have a switched
neutral.
Secondly in case of neutral/contactor failure the user will
have to change only the contactor instead of the whole
breaker
However when only one DG set is used we always go with 4
pole breaker.
Is This Answer Correct ? | 1 Yes | 5 No |
where used impendence relay?
Iam Preparing For Ap Transco Assistant Engineer (ELECTRICAL) Exam how To Prepare What Is The Refernce Books.can You Give The Advises To Me.tahnk You. This Is Radhika Iam Preparing For Ap Transco Assistant Engineer (ELECTRICAL
In order that work may be done:(a) Two wires are necessary(b) The circuit must have a switch(c) Coal must be burnt(d) A supply of energy is required
corona happens more in summer or winter?
15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ? and what will be per phase current for 15 kva
Is phase preventer require when overload relay is there
Load break swicth maintenance procedure.
Who is the first Bangladeshi Everest climber? Where is his home district?
H.t motor 6600 volt to same motor lt supply 440volt supply applyed to h.t motor to effect....
How to calculat the ratio of HT\LT in energy meter
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?