while doing the excitation current test on power
transformer what is the value of voltage to be applied?
Nomonal rated voltage or 10% of rated voltage? Is it
necessary to apply on high voltage side?
Answer / guna
we have to apply three phase voltage only..bcoz,for
transformer rated voltage is 220kv not 230v.we can check in
l.v side also.
| Is This Answer Correct ? | 5 Yes | 1 No |
What is E.M.F ?
How Id and Ires are calculated in siprotech 7ut612 and abb trsfmr differential relay.what is the formula
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
how to calculate the MF in meter reading
what is Insulation monitoring device. where it is used? (in switchgear room or control panel or in field equipment)
WHAT IS A DIFFERENCE BETWEEN A DC GEAR MOTOR AND STEPPER MOTOR.AND WHICH IS MORE APPROPRIATE TO USE FOR POSITION CONTROL PURPOSE?
what is the mechanical safety of DG ?
what is the difference between skin effect
How to calculate the value of capacitance of a capacitor used in power factor improvement plant if we know KVAR and voltages?
what is droop control?
Procedure for conduting vector group test on power transformers.why it is conducted?
in three phase 11kv transformer (11kv/433v) input( R,Y,B) output (X,Y,Z,N) the connection as follows 1 phase R -open 2phase y connected to both R and y of input] 3phase B- B what is the output voltage X to N ,Y to N , Z to N
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)