while doing the excitation current test on power
transformer what is the value of voltage to be applied?
Nomonal rated voltage or 10% of rated voltage? Is it
necessary to apply on high voltage side?
Answer / guna
we have to apply three phase voltage only..bcoz,for
transformer rated voltage is 220kv not 230v.we can check in
l.v side also.
| Is This Answer Correct ? | 5 Yes | 1 No |
how to calculate the load on transformer..????
I want to give Power supply to a house from the Feeder, Total Load of the House is 128 KW, how to calculate cable size for this load ?
What will happen if the rotor of an induction motor is fed from a 3 phase supply and the stator short circuited ?
Why CBCT rating is 50/1A
What is difference between potiential,volatge and emf
why star point of HT motor not earthed?
What is expention fastener (Fan)
whta is difference between contactor and breaker.
can you explain the rms value in simple words....
what iz second and fifth hormonics please explain
what is the rating of power generation in india?
is it possible to flow a current between nutral and earth in a circuit? although nutral and earth having same potential diffrence? i=0/r=0A if any body now any solid reason because i am getting a triping problem in rcbo due to nutral and earth shorting???
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)