Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

IF we have 500kva transformer 11.0/0.415V, 50Hz. How to
calculate the current on HT & LT side, how can we consider
for its breaker (HT & LT both)? You are requested to solve
the question herewith.

Answer Posted / antaratara ghosh

current on HV side= 500/(1.732*11)
= 26.24 A

current on LV side= 500/(1.732*0.415)
= 695.6 A

Breaker on HV side will be 630 A VCB (since it is the
lowest available VCB and in HV side you have to go for
VCB/SF6)

Breaker on LV side will be =greater than (1.2*695.6)A i.e.
834.72 A
so we consider it to be 1000 A ACB

Is This Answer Correct ?    19 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What magnetic circuit is formed in berry-type constructions and why?

1014


How to test IR testing & magnetic balance test

1939


how open delta PT works & what is its construction?

2194


how to differentiate a mpcb,mcb with a contactor? Explain their working operation

2135


What are the special cables required for explosion proof wiring?

3510


how to electrically make connection to ferroli GN2N?

1883


What is oscillator circuit?

1083


which fault is severe and why?between lll fault and lllg fault which fault is severe and y?

2455


what is the requirement regarding earthing of Single conductor with AWA

2170


In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?

1885


hi frnz,can somebody give me any project work? i am a 2nd year student & interested in practical works...plz give me some projects

1939


explain the Trip supervision circuit

2094


The magnitude of sum of two sinusoidal av voltage is equal to 230 volt.the magnitude of each individual voltage is also equal to 230 volt.what must be the phase difference between voltages?

1569


What is the basic of DTH.

2259


What are the advantages of instrument transformer?

1086