how is a displacer type level transmitter calibrated.explain the method?
Answers were Sorted based on User's Feedback
Answer / a.moin
A displacer type level is most commonly level application
used for the closed vessel as well as interface level where
the two process liquid having diffrent specific gravity.
Its works on the arthmedics principle or the loaw of
buoncy, the law say the weight of the substance immerse in
the liquid is equal to the amount of liquid displaced by
the body.
Now as per the question the way to calibrate the displacer
level first we have to isolate the level troll chenber from
its process by isolating the root valves,
then drain the liquid presence inthe chamber, connect the
PVC transparent tube at the bottom of the cahmber and then
start filling the water in the tube.
For zeroing
fill up the water into chember and adjust the zero check
this function two or three times....
compensate the S. G of diff liquids Prcoess S.G= 0.7 and
water S.G= 1.0
to calibrate the transmitter for span 0.7/1.0 *100= 70%
fill the water upto 70% adjust the span
For dry calibration of displacer you should knwo these
details below
Displcer weight: 2400 grms (2.4Kg)
volume of Displacer: 1620.84 by ^r2h..
displacer diameter: 7.620 centimeter
length of displacer: 35.56 centimeter
Note: the limitation of displacer cannot be exceed more
than 72 inches....
Is This Answer Correct ? | 20 Yes | 4 No |
Answer / haridass kwt
To calibrate the displacer type LTs by fixed in the w/bench,
First remove the head, clean displacer and chamber and
assemble,
fix the calibration setup (drain isolation, clear tube and
marked scale),
Calculate 100% position of fluid filling, by the Sp.
gravity of the fluid where the LT being used. (Ex: If sp.gr
is 0.8, then the 80% of the displacer height to be marked
in chamber due to the water used for calibration), and mark
every 25% in chamber ouside for reference.
Fill the water and check the transmitter/board/sensor
response approximately.
Fill the water till the displacer touches. and chk 0% and
adjust to 4mA.
Fill the water till 100% to check span and adjust 20mA.
(If the LT s not responding, replace LVDT/board and chk)
Repeat zero and span check 4-5 times and the chk every 25 %
rising and falling.
If ok, the prepare the calibration report and tag it.
Is This Answer Correct ? | 11 Yes | 1 No |
How to calibrate smoke Dectector
Explain the working of an electronic level troll.
What are the logic behind 2x2 and 2x3 logic and more when ask in interviews
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?
How to Calibrate Coriolis Flow transmitter in field
Why we use 4 - 20 ma?
what does mean by analog output trim and where this one used for?
why we use only 4-20 ma signal as AI and not 0-20 ma?
2 Answers Honeywell, Oil and Gas Jobs,
What is the definition of direct acting valve & reverse acting valve
in which mode of the zener diode act when load voltage is approximately constant
What is frequency factor in massflow meter? When using frequency output?