Answer / javed butt
At starting point(generator output) ref circuit is called
neutral. When we use phase & neutral in a circuit(2 wires
only) and connect same neutral wire with case as a ground,
it will work. But if phase and neutral and enterchanged,
then case will become hot and will be dangrous for the
humen life. When a separate earth wire is connected to
neutral at generator's out put and earth wire is run
separately and connected to the case, it will remain ground
even if the supply (2)wires are interchanged. In case of
leakage (hot to the ground) it will blow fuses and protect
the humen life.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / baisakhi ghosh
ground or earth in a miai electrical wiring system is a
cnductor that provides a low impedence to prevent hazardous
voltages from appearig on euipmwnt.norally a grounding
condutor does not carry current.
Neutral is a circuit conductor (that carries current in
normal operation), which is connected to earth (or ground)
generally at the service panel with the main disconnecting
switch or breaker..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anto maria jones
neutral is a return path, when a circuit having positive
and negative when the current flowing to positive and then
closed to the negative terminal, it is a closed circuit.
but earthing is a protecting the human body,earth is
actually connected to the body of the electrical equipments.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kaushlendra
at the genereting stations the conductor which is grounded
very deeply is known as neutral.actually we require two
terminals for a equipment to operate.one is phase and other
is neutral.the current enters through the phase conductor
and leaves through the neutral conductor.but the equipments
like press,cooler have three terminals.the third one is
earth.earth conductor is connected to the body of the
equipment ended in the ground(means we take a long rod and
insert into the ground deeply,so that it does not heat).
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anish baba
OBVIOUSLY, NEUTRAL IS REFRENCE POINT.IT GIVES INFORMATION
TO US THAT HOW MUCH VOLTAGE WE R USING WITH RESPECT TO
NEUTRA.....GROUND IS A MEDIUM BY WHICH LEAKAGE
CURRENT/VOLTAGE PASS TO EARTH.......GROUND ALSO INCREASES
THE VOLTAGE.........
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / azad
earth : this is the low impedance path for the higher values of currents which is connected to the ground.
neutral : this is the return path for the current as we know that current always flow in the circular direction.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pieter
Earth is an electrical conductor solidly connected to a
grounded peg or typically to a galvanised steel water pipe.
Neutral is a connecter to the star point of a three phase
power supply where all three phases are joined. If the three
phase load is balanced, there will be no current flowing in
the neutral conductor. The neutral conductor runs from the
appliance to the neutral point of the supply transformer.
Earth leakage protection devices monitor the current flow
from the Neutral conductor to earth though an earth leakage
detector device. If a leakage current is detected, it
indicates a faulty, and therefor a dangerous situation. The
earth leakage device will trip the mains as a safety precaution
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / r.s.sathe
Neutral is neccessary for circuit without its not circuit complete but Earth working in circuit abnormal condition like over current short circuit as well as earth for human body and machine protection.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kumaravel
neutral : All earthing point is connected to one point is known as neutral (power station)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nitish kumar
according to me earth can be treated as 0 potential point,
which is used for safetey of human being. whereas neutal is
a reference point, its potential can be 0, 0.5, 5,6,1000
etc. and it is also used as a return path for electrical
circuit.
| Is This Answer Correct ? | 3 Yes | 3 No |
sir plz send some previous year questions of jspl.
Why current shoots up in the secondary on the knee point voltage during saturation test of CT? How core saturation effects the secondary current (while the primary side is open)? What the logic behind this?
what is the difference between earth and neutral?
56 Answers Bhel, Emerson, HCL, JLL, L&T, Siemens, TVS,
If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma
what happens if number of poles in stator and rotor windins of slip ring induction motor are not same. Will it rotate near to the synchronus speed defined by stator?
How can you start-up the 40w tube lite with 230v AC/DC without using any choke/Coil?
line diagram for mcb , mccb , rccb .
What is transister , thermister , thyrister? what is its function? where this using?
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
Why using synchronising methed in DG's sets?
Why secondary of a CT in a power system acts as an open circuit after core saturation?
can we install HT panel & LT panel side by side or how much clearance is required ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)