I've descovered that when the earth wire in a domestic
electrical installation is not connected back to the board
(ground) a voltage of between 9-24v is is found to be
present in the earth wire.
When connected at the board there is no voltage - is this
normal and why does it happen?
Answers were Sorted based on User's Feedback
Answer / prof. dr. k. manjunath
The correct answer is there is no path for the leakage
current. If domestic power consuming power apparatus earth
connection is connected to the board, the correct ground
connection offers zero resistance to the leakage current.
This is the effect that, you noticed zero volts when
connected to the board.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kj
You will find that no insulation is perfect. There will
always be some leakage. As well there will be induction
into the wire because it is run next to the phase and
neutral. Both of these can account for a voltage in the
earth wire when disconnected.
I would expect a higher reading if the voltage was due to
leakage in the insulation. This could be up to phase
voltage but with no current capacity.
I would think the reading is most likely induction. The
voltage here would increase depanding on the current and
the length that the earth was run with the phase and
neutral.
When it is connected to the earth in the board the voltage
is drained away as in both cases there is only negligible
current capacity.
| Is This Answer Correct ? | 0 Yes | 2 No |
What happens if 25 Hz frequency is applied for 400/200,50 Hz single phase Transformer.Will Voltage increase ?
2 Answers Bhel, Dawlance, IBM,
how to test generator protection rotor earth fault relay and locked rotor test?
what is the significance of tan&delta and how it performed in power transformer
what is the main difference b/w contactor and relay
2 Answers Pace Pharmaceuticals,
define as synchronous generator
What will happen when we connect 2 bulbs in series between 2 phases
What is notching in dc machine?
which IS or IEC is used for earthing,breakdown voltage of transformer oil, hv/pd testing and all type of electrical testing
State the function of control rods used in nuclear reactor
where was current transformer protection units used and why??
why in some cases the receiving end voltage is higher than the sending end voltage in transmission line (called 'Ferranti effect') ????? whts the reason behind tht???
Why the airgap of an induction motor is less compared to that of a synchronous machine?
4 Answers MGVCL, RRB, WebTech,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)