If any control valve create hunting problem, what is the
possible reason and solution?
Answers were Sorted based on User's Feedback
Answer / imran
check as
1-put the controll valv in manual and check incoming signal
if stable then problem in controll valve
2- check positioner condition its feedback link ,incase of
smart poistener check feedback potentiometer.spring and
configration.
3-check diaphragam
4-gland packing
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / bhavesh
check the gland packing,check the positioner o/p is
unstable,check the small leakage on actuator.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / muhammad arsalan afzal
1=First of all check the feedback link of positioner mostly
such type of problem occur due to feedback link looseness.
2=Gain of the controller is too high you have to adjust it.
3=Gland packing is too tight slightly lose the gland pusher's
screws.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / s.k.bakshi
1. First check the positioner air supply and the positioner.
2. If problem persists tune the PID.
| Is This Answer Correct ? | 8 Yes | 7 No |
Answer / suman chakraborty
check I/P signal means I/P and O/P whether the AFR o/p of I/P is stable or not.and check the AI Chanel of I/P.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dhaval joshi
First check actuator position..removed power from the
actuator...and accordingly connect first power supply
cable,after connect command and feedback cable.
| Is This Answer Correct ? | 1 Yes | 6 No |
as an instrumentation engineer which are the things we have to know / or we must have idea about that....
How to calibrate displacer type level transmitter (chemtrol make )for level measurement in hotwell , LP & HP heater ?
any body please send me the old question papers of ongc test.
How will you calibrate an Absolute Pr.Transmitter of range 400mmHg absolute ?
how does we do bench calibration of a differential transmitter.
Identification of control valve parts.
0 Answers CCIE, Oil and Gas Jobs,
how to write the program for single push button by using ladder diagram
HOw To Use 24V DC in Instrument?
If the on Of the DO module is off in the System cabinet, then what is the Procedure to check weather the Module is working or not.
which instrument is used to study the structure of phloem and xylem tissue?
what will be the principle & application of dissoled oxygen analyzer at wast water treatment plant at oxidation basin & how it work?
Calibration procedure for Electro magnetic Flow meter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)