If any control valve create hunting problem, what is the
possible reason and solution?
Answers were Sorted based on User's Feedback
Answer / imran
check as
1-put the controll valv in manual and check incoming signal
if stable then problem in controll valve
2- check positioner condition its feedback link ,incase of
smart poistener check feedback potentiometer.spring and
configration.
3-check diaphragam
4-gland packing
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / bhavesh
check the gland packing,check the positioner o/p is
unstable,check the small leakage on actuator.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / muhammad arsalan afzal
1=First of all check the feedback link of positioner mostly
such type of problem occur due to feedback link looseness.
2=Gain of the controller is too high you have to adjust it.
3=Gland packing is too tight slightly lose the gland pusher's
screws.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / s.k.bakshi
1. First check the positioner air supply and the positioner.
2. If problem persists tune the PID.
| Is This Answer Correct ? | 8 Yes | 7 No |
Answer / suman chakraborty
check I/P signal means I/P and O/P whether the AFR o/p of I/P is stable or not.and check the AI Chanel of I/P.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dhaval joshi
First check actuator position..removed power from the
actuator...and accordingly connect first power supply
cable,after connect command and feedback cable.
| Is This Answer Correct ? | 1 Yes | 6 No |
model question paper of instrumentation for Jindal GET 2010.plz reply sudhanshukumar08@yahoo.com
what is lead lag compensator and for wat v using that???
What is loop checking ?
10 Answers Kharafi National, Petrofac, Samsung,
what is pyrometer? which purpose it has to be used?
how to calculate flow range in DP tx
Specify for Cables - Flame Retardant and Fire Resistant?
NAME ANY TWO ELASTIC PRESURE SENSOR?
Generally in which location ( JB or IO card or DCS) the thermocouple compensation is done.Also where they measure the atmosphere temp ( for compensation) in JB OR DCS panel? How they compensating that atmosphere temp? is any circuit for that ( like in rtd wheatstone bridge)?
why we use sensing type(NPN)on a vibration monitring system not a (PNP)sensing type
if found error in magnetic flow meter?how can we adjust?
2 Answers ANI Instruments, Techint,
what is compensation in engineering and what is temperature compensation?
What is the difference in clamp on type and inline type ultrasonic flow transmitter.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)