One 15kw motor Why we used star delta feeder?why not used DOL
please explain in details
Answers were Sorted based on User's Feedback
The star delta starter limits the starting current of the
motor by reducing the voltage across each winding. In star
the voltage is equivalent to the phase to neutral of the
power supply. In delta the phase to phase voltage is
applied across the windings.
With a DOL starter the phase to phase voltage is applied
across the windings. The starting current can be in excess
of 7 times the full load current.
The main reason for using star delta starters is that the
power supply system to the motor does not have to support
the high current needed for DOL starting. If the power
supply is not able to supply the current a voltage dip will
occur affecting all other users on the supply.
| Is This Answer Correct ? | 11 Yes | 1 No |
We can use dol stater up to 5HP (dol stater can
not control starting current of motor but protect
by them up to 5HP). We have been using dol
staters to lower rating ac motors due to low cost.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / vijendra joglekar
The Main purpose of using starter in motor to limit the
starting current as you know evry starter have there own
limitations i.e rating,inrussh current holding capacity as
you told 15 kw motor cant use DOL starter because of its
limitaions its not with stand motor rated current .
| Is This Answer Correct ? | 0 Yes | 8 No |
what is the working principle of UPS?
what is derating factor in Cable ? how we minimise this?
18 Answers Bhel, College School Exams Tests,
How to test the vector groups of 3 winding transformer & phase displacements
in case of transformer the power factor is depend on input or the output
define the active power?
12.5 KVAR capacitor 440V gas filled, Its used for windmill purpose, How can i know about microfarad value for this capacitor
how to convert 1 phase power to 3phase power by using induction motor. . . .
1)how to reduce the value of tan delta of trasformer and CB,bushing,CT&PT,CVT ? 2)how to reduce the resistance of CB contact and its operating time? 3)plz.....send me the project report on conditioning and monitoring of substation equipment on my email id (gusaiyogendra03@gmail.com)
Why we Specify Transformer rating 433 V Instead of 415V ?
Did RMU have ct and pt ?
why are maintine power factor 0.99 in Eb line? why are used capacitor bank in Eb line? what is the purpose capacitor bank?
4 Answers TNEB Tamil Nadu Electricity Board,
How to identify Motor leads in their order coming out from winding without tag (U1, V1, W1 & U2, V2, W2)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)