One 15kw motor Why we used star delta feeder?why not used DOL
please explain in details
Answers were Sorted based on User's Feedback
The star delta starter limits the starting current of the
motor by reducing the voltage across each winding. In star
the voltage is equivalent to the phase to neutral of the
power supply. In delta the phase to phase voltage is
applied across the windings.
With a DOL starter the phase to phase voltage is applied
across the windings. The starting current can be in excess
of 7 times the full load current.
The main reason for using star delta starters is that the
power supply system to the motor does not have to support
the high current needed for DOL starting. If the power
supply is not able to supply the current a voltage dip will
occur affecting all other users on the supply.
| Is This Answer Correct ? | 11 Yes | 1 No |
We can use dol stater up to 5HP (dol stater can
not control starting current of motor but protect
by them up to 5HP). We have been using dol
staters to lower rating ac motors due to low cost.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / vijendra joglekar
The Main purpose of using starter in motor to limit the
starting current as you know evry starter have there own
limitations i.e rating,inrussh current holding capacity as
you told 15 kw motor cant use DOL starter because of its
limitaions its not with stand motor rated current .
| Is This Answer Correct ? | 0 Yes | 8 No |
what is the cable capacity of any load wise .
Explain how Hormonics will effect the Electrical System?
a 11 kv line is grounded and a 110 kv line is grounded. which line have the greater current flow?
what are the range of memory address in plc for L&T lx7 4A
describe the fully control circuit diagram of ac drives
why we avoid parallel operation of diesl generator?
The purpose of a choke is to provide a ?
In a Capacitor the electric charge is stored in:
2 Answers TELK Transformers And Electricals Kerala Limited,
A well system is when , no. of bus bar is less or more. Tell me the concept of it.
what is the difference between megger and earth tester?
28 Answers Ashok Leyland, IOCL, RRL,
can i use 2000/5A Clamp meter to measure HT cable
In an panel board if the outgoings are power plugs and motor equipments...what should we choose as the incomer of the of the panel board?? MCCB OR ISOLATOR?? Should we use ELCB protection??if so where??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)