There is a problem with our HART475 it is not communicating
with smart devices error becomes "NO DEVICE FOUND"we have
insert 250ohm resistance as per requirement but invain plz
tell me the solution?
1) How do you know that the device talks HART? Many field transmitters talk Brain, Honeywell DE, Foundation Fieldbus, Profibus or 4-20mA only.
Have you confirmed the HART functionality on that device?
2) Point-to-point (communicator-to-transmitter) is usually done with the device at address 0 and with the communicator polling address 0.
Is the communicator polling address 0?
Is the device at address 0?
3) On many transmitters, HART can be disabled. Is HART enabled on this transmitter?
4) The transmitter has to be powered, initialized and in its operating mode in order to communicate via HART. Sometimes transmitters are not powered, but when connecting from the a marshalling panel, it is obvious, because the transmitter is remote location. Is the transmitter powered and operating?
5) Are connections across the dropping resistor or across the transmitter's (+) or (-) terminals? Connecting across a pressure transmitter's 'test' terminals will not work properly for HART communication.
6) A loop isolator module that is not specifically designed for HART will strip off the HART signal, but pass the 4-20mA current signal. If a loop isolator is installed in the loop, is it designed for HART operation.
7) If the power supply ripple and noise exceeds the HART specification, the power supply noise will interfere with HART or prevent communication entirely.
8) The 475 can have 3 terminals at the top where the banana plug field cable plugs in. 2 terminals are for HART, 2 terminals are for Foundation Fieldbus (FF). If the cable is plugged into the 2 terminals for FF, HART communications will be blocked by not having a cable in the correct port.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Anybody can tell me how to convert mmHg2o /psi to scfm please give me formula of conversion
How do understand by hart protocol?
4 Answers BW Instrumentation Electrical,
Why do we floating DC in DC system.
DCS marshilling Cabinet Power supply can be replace during plant running time?
can you tell me how many stages in steam turbine of 10 MW power plant
use of split range ? where it is used ? in which control loop it is used ?
i want know about capillary type LT transmitter installation. we can install any location in between to HP and LP leg?
How to convert gpm into inches of eater.I nerd formula with example so pls help me.
Give 2 application of quartz crystal used for process parameter measurement.
the square root type transmitter r used to which applications
State four different types of flow measurement, for gas flow measurement MMSCFD is the common unit expand the unit and specify significance of word S in the unit.
in DCS or PLC we can not put all ai or di,there is calculation through which we can accomodate certain no of digital and analog signal.I need to know that calculation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)