1) How do you know that the device talks HART? Many field transmitters talk Brain, Honeywell DE, Foundation Fieldbus, Profibus or 4-20mA only.
Have you confirmed the HART functionality on that device?
2) Point-to-point (communicator-to-transmitter) is usually done with the device at address 0 and with the communicator polling address 0.
Is the communicator polling address 0?
Is the device at address 0?
3) On many transmitters, HART can be disabled. Is HART enabled on this transmitter?
4) The transmitter has to be powered, initialized and in its operating mode in order to communicate via HART. Sometimes transmitters are not powered, but when connecting from the a marshalling panel, it is obvious, because the transmitter is remote location. Is the transmitter powered and operating?
5) Are connections across the dropping resistor or across the transmitter's (+) or (-) terminals? Connecting across a pressure transmitter's 'test' terminals will not work properly for HART communication.
6) A loop isolator module that is not specifically designed for HART will strip off the HART signal, but pass the 4-20mA current signal. If a loop isolator is installed in the loop, is it designed for HART operation.
7) If the power supply ripple and noise exceeds the HART specification, the power supply noise will interfere with HART or prevent communication entirely.
8) The 475 can have 3 terminals at the top where the banana plug field cable plugs in. 2 terminals are for HART, 2 terminals are for Foundation Fieldbus (FF). If the cable is plugged into the 2 terminals for FF, HART communications will be blocked by not having a cable in the correct port.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
what is meaning of software redundency and hardware redundency?
What is Span Error
what is wave length were using ?
what is exat meaning of compentation in RTD ? what diffrent between 2 wire,2 wire and 4 wire RTDs?
Can 2 transmitters be connected to Integral orifice meter taps? Does an integral orifice comes with 2 set of taps?
How to connect PLC to DCS ?
what are turbo generators?
Explain working principle of lvdt?
Hello Friends do you know this answer of this Question? Which color you would use when there is Somthing not correct or need to change In P&ID? i mean color that use for highlight that need to update in P&ID. Yellow Highlighter ? Red color ? Blue Color ? Appreciate for your answer. Thanks Blue Color
how to measure level under ground tank ? which type of transmitter very accuracy ?
In turbine, what does term CDP, NI, NH, HSSOC, means
why we r opening HOT BYPASS valve during startup of a compressor?