IN star -delta motors normally first operated in star
mode {absulated given (r-y-b) phases after one miute change
in delta mode in this case i am change phase sequience for
example R -PHASE TO CHANGE Y-PHASE ;Y-PHASE TO CHANGE
R-PHASE SO THIS TIME MOTOR WILL HAPPEN RUNNIG MODE
EIGHTER(OR) STOP MODE(TRIP MODE)
Answers were Sorted based on User's Feedback
motor will stop and triped because motor will try to run in
opposite direction
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / asif.k64@hotmail.com
The motor will run in opposite direction.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / dinesh.n
It will not stop and Trip...It will running in the opposite direction.Once we change the Phase motor running in oppsite direction only..
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / sundaresan044
STOP AND TRIP It will running in the opposite direction.Once we change the Phase motor running in oppsite direction only
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ankit.vats01
moter will be trip cause motor will run apposite direction
suddnly so motor will be trip
| Is This Answer Correct ? | 0 Yes | 1 No |
what is mutual induction principle?
what do you mean by every IC 74 first digit.why are you using this no.why not using another no.
Which motor has high starting torque
iam interesting to design the control panel for 3 phase pump motors by controling single phase switches.iam plan to use fuse,contactor & relay for motor protection .how can i select the voltage & amps rating for fuse,contactor & relay plz guide me .if anybody clarify my doubt means it will more helpful for my future .
how to calculate
What kinds of decision are made about CT from it's Knee point(voltage & current)?
What is the specification of service line (ie from electrical post to cut out) used by electricity boards used in india.i mean which material,its size etc.. please give the answer at lalkishan.p@gmail.com
can we use inductor in case of d.c.,if yes then what will happen in circuit
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
how can we select the type of wire.what factors we have to look on it , do we have some formula to calculate it. please guide me on it
I WANT HOW CALCULATE TO CABLE FOR WELDING PLANT ?
what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)