On a 10 KVA UPS we have to provide a DC MCB for Battery bank
of 16 nos (12 V 65 AH).
What Shall be the current rating of DC MCB ?
Answers were Sorted based on User's Feedback
Answer / kathirvelan.j
Battery banks are always connected in series so the total
voltage of the battery bank will be
12*16=192V
10KVA=10000VA
A=10000/192=52 Amps
But we need to consider the safety margin of atleast 125%
on the MCB rating and also there are only standard current
ratings are only available in the market so by considering
all these reason we can go for a 65Amps DC MCB.
Is This Answer Correct ? | 16 Yes | 0 No |
Answer / asif.k64@hotmail.com
UPS is 10 KVA, and battery is 65AH
Hence if it is a 1 phase UPS
KVA = V*A
10000 = 240*A
A= 10000/240
A = 42 A full load
Approximately a 63 A MCB would be required
Is This Answer Correct ? | 21 Yes | 7 No |
Answer / ravi v nair
Battery banks are always connected in series so the total
voltage of the battery bank will be
12*16=192V
10KVA=10000VA
A=10000/192=52.08
we need a 55A DC MCB
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / naveen kumar.b
Ans:- 60Amps MCB
how:-
for 16 battery net voltage is 192Vdc.
For battery low cut OFF voltage fixed in by all kind of ups is 10.5 each battery . so for 16 battery System battery low cut of votage is 168VDC
( :- at time low battery voltage only Dc current consumption is high, we need to take maximum current consumtion for select MCB)
total load we taken= 1oKVA Full load.
DC voltage at time low battery = 168
current consume (at time of low batter)= 10000KVA /168Vdc
current consumption is 60Amps arround
so 60Amps MCB is required
Is This Answer Correct ? | 2 Yes | 0 No |
Why transformer rating in KVA? and Generator also?
6 Answers Bhel, IEEE, Toyo Denki, Toyo Engineering,
DG SET BLOCK DIGRAM
what is use of substation? Any book on how to instal or construction of substations?
In a power conditoining unit (inverter) of a solar plant when we measure the d.c. current fed by different strings of solar plates to inverter, the current in the negative wire is less almost by 1 ampere to the current in its positive wire say current in positive wire 5 A , then current in negative wire of the same string is 4 A. Since the current entering should be equal to current leaving then why the current is noticably less in negative wire.
if single phase is having 220v supply then why three phase is having 440v instead of 660v?
Classify drilling machines.
what is advantage of providing taping on HT side?
IN CONTROL SYSTEMS Y WE NEED TO KNOW THE STABILITY OF THE SYSTEM?WHAT IS ITS PRACTICAL USE?
What happen if ac supply is fed to rotor of the alternator?
what is the working of air compressor.
how to calculate the watts from the tr
If the rated speed of a d.c. Shunt motor is1440 r.p.m, which method of speed control would you suggested to obtain a speed of 1500 r.p.m?