Answer / kathirvelan.j
Battery banks are always connected in series so the total
voltage of the battery bank will be
12*16=192V
10KVA=10000VA
A=10000/192=52 Amps
But we need to consider the safety margin of atleast 125%
on the MCB rating and also there are only standard current
ratings are only available in the market so by considering
all these reason we can go for a 65Amps DC MCB.
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / asif.k64@hotmail.com
UPS is 10 KVA, and battery is 65AH
Hence if it is a 1 phase UPS
KVA = V*A
10000 = 240*A
A= 10000/240
A = 42 A full load
Approximately a 63 A MCB would be required
| Is This Answer Correct ? | 21 Yes | 7 No |
Answer / ravi v nair
Battery banks are always connected in series so the total
voltage of the battery bank will be
12*16=192V
10KVA=10000VA
A=10000/192=52.08
we need a 55A DC MCB
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / naveen kumar.b
Ans:- 60Amps MCB
how:-
for 16 battery net voltage is 192Vdc.
For battery low cut OFF voltage fixed in by all kind of ups is 10.5 each battery . so for 16 battery System battery low cut of votage is 168VDC
( :- at time low battery voltage only Dc current consumption is high, we need to take maximum current consumtion for select MCB)
total load we taken= 1oKVA Full load.
DC voltage at time low battery = 168
current consume (at time of low batter)= 10000KVA /168Vdc
current consumption is 60Amps arround
so 60Amps MCB is required
| Is This Answer Correct ? | 2 Yes | 0 No |
why transmission line towers are longer than communication line towers?
which oil is used in transformer?
Why the colour of insulator is always is chocolate in colour?
how to calculate the voltage drop in electrical cable while laying cables?
what bridge circuit is used in Tandelta circuit
installation of subsatation of33kv
what is the reason of capacitor failure in alternator which is working with 10 kva dgset
what are the types of transformers
What is the high series capacitance winding on high voltage power transformer ?
why use delta star x-mer in distribution system.
PLC Based Process Automoation Panels?
why and how voltage sharing in transformer, during magnetic balance test ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)