Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


On a 10 KVA UPS we have to provide a DC MCB for Battery bank
of 16 nos (12 V 65 AH).
What Shall be the current rating of DC MCB ?

Answers were Sorted based on User's Feedback



On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall b..

Answer / kathirvelan.j

Battery banks are always connected in series so the total
voltage of the battery bank will be
12*16=192V
10KVA=10000VA
A=10000/192=52 Amps

But we need to consider the safety margin of atleast 125%
on the MCB rating and also there are only standard current
ratings are only available in the market so by considering
all these reason we can go for a 65Amps DC MCB.

Is This Answer Correct ?    16 Yes 0 No

On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall b..

Answer / asif.k64@hotmail.com

UPS is 10 KVA, and battery is 65AH

Hence if it is a 1 phase UPS

KVA = V*A
10000 = 240*A
A= 10000/240
A = 42 A full load

Approximately a 63 A MCB would be required

Is This Answer Correct ?    21 Yes 7 No

On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall b..

Answer / ravi v nair

Battery banks are always connected in series so the total
voltage of the battery bank will be
12*16=192V
10KVA=10000VA
A=10000/192=52.08
we need a 55A DC MCB

Is This Answer Correct ?    7 Yes 2 No

On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall b..

Answer / dhanesh kumar

ans is roung

Is This Answer Correct ?    6 Yes 3 No

On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall b..

Answer / naveen kumar.b

Ans:- 60Amps MCB

how:-

for 16 battery net voltage is 192Vdc.

For battery low cut OFF voltage fixed in by all kind of ups is 10.5 each battery . so for 16 battery System battery low cut of votage is 168VDC
( :- at time low battery voltage only Dc current consumption is high, we need to take maximum current consumtion for select MCB)

total load we taken= 1oKVA Full load.

DC voltage at time low battery = 168

current consume (at time of low batter)= 10000KVA /168Vdc

current consumption is 60Amps arround

so 60Amps MCB is required

Is This Answer Correct ?    2 Yes 0 No

On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall b..

Answer / hkrish.eee

1.5A

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what is the advantage of pwm pulse compare to squarewave pulse.

2 Answers  


ple send to the how to improve the efficiency & economical to the thermal power plant

1 Answers  


what is IP55,IP65

4 Answers  


3phase motor 400v (induction) A.C 4kw company design 1400rpm but our requirement 2000rpm possible? attached any instrument. reply fast! contact 03343262442

3 Answers  


what is relation between ct and pt ratio with multiplication factor of a energy meter? is there any other factor on which multification factor depend?

0 Answers  


why commutator are not used in rectification purpose in power electronics?

1 Answers  


What is the function of isolater

4 Answers   Getco, Gland Pharma,


what mean ohm

1 Answers   Shoba Devlopers,


At what voltage domestic tubelight works?

2 Answers   Cigfil, L&T, MNC,


how can decide the current rating of oltc

0 Answers  


Can anybody tell abt concrete encased earthing or grounding?

0 Answers  


sir what is the minimum IR value of 11 KV alternator?

4 Answers   Kirloskar,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)