Answer / sennapparajan
Master trip realy is the main trip relay.The breaker will
trip through This relay only. in transmission &
disttribution line there are so many protection relays
like....distence relay overcurrent earth fault,
diffrential. All the relay'S contact will connet parelly to
master trip relay. if any of the protection rely sence the
fault... it will energise the master trip rely and the
master trip relay will trip the breaker.it got one more
name like lock out relay.
| Is This Answer Correct ? | 197 Yes | 18 No |
Answer / linu mohan
master Trip relay 86 is the main tripping relay in the relay
protection scheme.It is actually tripping the breaker
poles.It acts because of the stimuli from any of the
protection relays.It's tripping coils are related with the
actuators from different relays.For example Directional
overcurrent relays and earth fault relays
| Is This Answer Correct ? | 57 Yes | 10 No |
Answer / satya rout (oeg rr)
In a transmission &
disttribution system a high voltage line there are so many protection relays are used
like-distence relay, overcurrent & overvoltage rly, earth fault rly,
diffrential rly . All the relay'S are connet paralley to
master trip relay. if any of the protection rely sence the
fault... it will send a voltage signal ,then energise the master trip rely coil and the
master trip relay will trip the breaker.
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / vinod
FUNCTION- Master trip relay 86 main function is to pick up the trip coil of the circuit breaker, relay 86 pick up if any of the protection relay of the respective feeder or equipment operate.
86 relay is a manual reset relay (its avoid multiple charging of the faulty system with unknown operators)
USAGE: The relay pick up through the protection relay contact(static or numerical) have less current rating, it can not carry the trip coil current of the circuit breaker
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / k.prakashchandra
If the trip relay has to open more than 1 cbs or circuits
,it is called master trip relay (86G)It is used in
protection of Trs and generators.
| Is This Answer Correct ? | 14 Yes | 45 No |
What will happen if supply frequency change in Transformer KVA rating ?
Can any body explain the operation system of MVWS(May be related to water and fire hydraunt system)?
Why derivative controller is not used in control systems?
why are installed water leakage detection system data centers & server rooms
Inductor and capacitor ........ power in one phase and ...... it in another phase. if any body found this gaps answer.please sent me to habib_eu2008@yahoo.com
Motor and transformer working with same principle so why motor rotates while transformer not?
I've descovered that when the earth wire in a domestic electrical installation is not connected back to the board (ground) a voltage of between 9-24v is is found to be present in the earth wire. When connected at the board there is no voltage - is this normal and why does it happen?
what is meaning volt-hz ration,where is necessry tomaintain and why. specialy during increase the power of generator.
practically What is power factor
What is difference between YNyn0 and YNyn ??
how to calculate capacitor rating for an induction transformer ex.for 12 mva furnace calculate capacitor rating
Define conversion efficiency of a power amplifier. What is its value for class c power amplifier?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)