what is the function of a Master
trip relay? why is it used ?
Answers were Sorted based on User's Feedback
Answer / sennapparajan
Master trip realy is the main trip relay.The breaker will
trip through This relay only. in transmission &
disttribution line there are so many protection relays
like....distence relay overcurrent earth fault,
diffrential. All the relay'S contact will connet parelly to
master trip relay. if any of the protection rely sence the
fault... it will energise the master trip rely and the
master trip relay will trip the breaker.it got one more
name like lock out relay.
| Is This Answer Correct ? | 197 Yes | 18 No |
Answer / linu mohan
master Trip relay 86 is the main tripping relay in the relay
protection scheme.It is actually tripping the breaker
poles.It acts because of the stimuli from any of the
protection relays.It's tripping coils are related with the
actuators from different relays.For example Directional
overcurrent relays and earth fault relays
| Is This Answer Correct ? | 57 Yes | 10 No |
Answer / satya rout (oeg rr)
In a transmission &
disttribution system a high voltage line there are so many protection relays are used
like-distence relay, overcurrent & overvoltage rly, earth fault rly,
diffrential rly . All the relay'S are connet paralley to
master trip relay. if any of the protection rely sence the
fault... it will send a voltage signal ,then energise the master trip rely coil and the
master trip relay will trip the breaker.
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / vinod
FUNCTION- Master trip relay 86 main function is to pick up the trip coil of the circuit breaker, relay 86 pick up if any of the protection relay of the respective feeder or equipment operate.
86 relay is a manual reset relay (its avoid multiple charging of the faulty system with unknown operators)
USAGE: The relay pick up through the protection relay contact(static or numerical) have less current rating, it can not carry the trip coil current of the circuit breaker
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / k.prakashchandra
If the trip relay has to open more than 1 cbs or circuits
,it is called master trip relay (86G)It is used in
protection of Trs and generators.
| Is This Answer Correct ? | 14 Yes | 45 No |
why names such like dog ,rabbit, osprey,ant are used for conductors.
How much must be gape bitween 2 cable on cable tray?
what the purpose of transmited high voltage in over head lines
I have a 5KVA UPS. Total load to be connected almost 3KW. Ordering a battery pack with capacity of 1920VAh. How long will the backup time be?
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation
What is the automatic voltage regulator with servomotor?
what r the checklist while installing a 380 kva DG set
how the harmonic pluses take place in the flow of current
What are two contours of nichols chart?
TRANAFORMER RATING 500 KVA,33KV/433, SECONDARY SIDE SWITCHED ON ONLY CAPACITOR LOAD 140 AMS, PRIMARY SIDE HOW MUCH VOLTS INCREASE?
what is subtransient , transient and steady stateac components
AVR is used for the Voltage regulation of the Generator using the feedback signal by exciting the field winding of the generator.But how the field winding will be excited & using what?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)