Answer / yusuf
> Opening and Closing Coil Resistance measurement
> Contact Resistance Measurement. (This Ensures minimum
Voltage drop)
> Timing Test(Ensures Fault clearance time)
> IR Measurement(Ensure proper Isolation from Ground and
between Phases)
Other than these, H.V, Flash Test, Tan Delta are also done
in the factory
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / manisand1
Above all some more test is to included i will clear this
in next time.
| Is This Answer Correct ? | 0 Yes | 0 No |
why we are having many type of vector group in the transformer ,what is the use of it?
hi... Can anybody give me description of type-2 coordination, IP protection, NEMA standards ? Thanks..
how the synchronizing is obtained at bus couplers in grid substation? (because there we cannot change the frequency in one of transmission lines like in generator synchronization)
What are the types of transformers according to the arrangement of iron cores?
WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?
13 Answers Tech Mahindra, Technip,
what will happen if the bus PT fuses are accidently removed from the circuit in 6.6kV feeder?
Why do we use series motor to start our car?
what is the capacity of storing mass electricity.
what are the checks of diesel gensets
how earth resistance can be improved in dry soil
what is stay bow?
What is type of transformers?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)