What are the types of TESTS in CIRCUIT BREAKERS based on
Testing and commissioning?
Answer Posted / yusuf
> Opening and Closing Coil Resistance measurement
> Contact Resistance Measurement. (This Ensures minimum
Voltage drop)
> Timing Test(Ensures Fault clearance time)
> IR Measurement(Ensure proper Isolation from Ground and
between Phases)
Other than these, H.V, Flash Test, Tan Delta are also done
in the factory
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
help me with the question that might be ask on the interview for technical position
What is the use of lag compensator?
What is mason's gain formula?
how to calculate voltage drop and followed by cable calculation?is there avail in formula?
what is mean by drives?
in cvt,there are two windings,1a,1n and 2a,2n.in my one project i use only one winding i.e.1a,1n. the other winding is not in use, so i connect it in open delta and want to close it by ibsertibg thermal resistor. the output of cvt is 132kv/115/sqrt3. plesae tell me exact value of resistor, so i may close it to avoid the resonance phenomenin. send me answer on this email adress please. aetcon-po@aetcon.com
when generator short circuit condition, the current how dissipates. or at short circuit voltage not available then current how can flow?
hi frnds...pls send me aptransco previous papers .....pls..pls,,,(madhar.rocking@gmail.com)and suggest me some websites
Give the topology of current amplifier with current shunt feedback?
How to calculate Temp from Resister from PT100 equation,
what should be the no load current for 3 phase ac motors ranging from 5 kw to 1000kw?
how much allowable resistance that can be difference in motor all coils?
what is the relation between reactive power and power factor for the what is the limit of reactive power and power factor
What is meant by impedance? difference between high & low impedance ?