how can we minimize the off load losses of a distribution
transformer which is required to be energized 24x7 ??
capacity of the T/F is 1250 KVA and off load losses are
around 2.0 KW.. can we use capacitor bank at the secondary
of such a T/F to overcome off load losses? please elaborate
briefly...thanks
Answers were Sorted based on User's Feedback
Answer / ahmad yousuf
need answers from Transformer specialists..!!
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shariff
Distribution transformers are to be charged 24x7 as they
have to supply to the consumers. These transformers are
loaded in a day ( 24 hrs) with different loads, i.e more
load during peak hours and light loads during off peak
hours. Whatever the load or no load on this trf the off
load losses will be present in the trfs and cant be
avoided. The capacitors connecting sec. will not help in
any way and that will be used only for the pf improvement.
Hence this trf efficency will be calculated as ALL-DAY
EFFCICIENCY... For more the the effciency the trf should be
loaded to its rating(100%). The noload (offload) losses
cant be supressed in the transformers as this is part of
the loss occurred to magntize the core.
Is This Answer Correct ? | 0 Yes | 1 No |
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
how to select energy meter? have any calculation?
WHAT IS THE DIFFERENCE BETWEEN AN ACB & mccb 7 WHAT IS THE CRITERIA WHEN TO USE WHICH OF THE TWO
Explain what is clipper and clamper circuits?
what should be the spaciing between street lights designed for a manufacturing location. any IS codes?
write a c++ code that receives an integer number and display the sum of the number and its revers integer?
should Dy11 and Dy1 group can be operated in parallel??????
I have 4 busbar of 1000 ampere. we use 4 busbar to make 4000 ampere in one phase.my problem is that when we applied 60% load on that then busbar produced high noise.what is the reason of that and how can i minimize that noise.
0 Answers College School Exams Tests,
why gravels is used in transformer yard?
What is meant by Active and reactive power?
8 Answers Micron Electricals, SVIT,
Load 380kva eb 415v,load amps 350.Same load dg 415v,load amps 420 what reason ?
1 Answers AVT Natural Products,
DESCRIBEPNEUMATIC SYSTM OF ASH HANDLING PLANT