How to calculate the Sizes of the cable required for one
specific load? Is there any formula for that? ( EX: For
400KW load,50mtr Length, What is the LT cable Size
required?)
Answers were Sorted based on User's Feedback
Yes we have formula.....
Power P =400KW, Length L =50 Mtr, Voltage V =415V
ANSWER:-------
First find current,
Current I= 695.65A
Apply the factors in the below mentioned formula:-
R = pL/a
Where R=Resistance, p=Resistivity, L=Length, a=Area
Since p=12 for Aluminiun and 14 for Copper.
Then, R= pL/a
We know that V=IR
Apply "R" in Ohms Law
V = IR
V = I pL/a
Therefore ,
Area "a"= (IpL/V) / 1.732 (since 3 phase)
a = (695.65 x 12 x 50 / 415)/1.732
a = 580.69 ( Approximately 600 Sq.mm )
a = 600 ( 2 x 300 Sq.mm)
Therefore 2R, 3.5C X 300 Sq.mm cable is required.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / noob
wat does 2R mean?
how did u get V = 415v?
50 meters is the length of wat?
the wire? the load?
| Is This Answer Correct ? | 2 Yes | 1 No |
why sometime we get electrical shock while touching the ballon of dish tv connection ? which we should not get.
What do you mean by passive circuit elements and why these are called passive?
what is the difference between RMS meter and normal meter
Hi, Next week Iam appearing RRB exam for section engineer. So help me to get modal question papers for this position. Iam very thankful to you. Whether question will be fully techanical format or general form. Please give me a details regarding this exam.
How voltage step down is done?
What is Ten Delta Test ?
What type of protective system we uses in L.V. distribution panels?
effect of single phase transformer on full load current?
Ceiling Fan and Storage type water heater. Discuss
why transformer ratings are taken in 11kv 22kv 33kv but not in 10,20,30kv
What will be the minimum megger value of 1700 KVA Transformer? a) Do megger value varies according to climate conditions and area . b) If megger value is 100 mega ohm is it good for new transfomer. Explain?
i am BSEE student, my project study is to synchronize the generator of an hospital, it have a one 313KVA standby-power diesel gen.,and three 100kva transformer.The generator system is operated manually and no ATS or UPS. one more new building is being build so the transformer will be upgrade to a higher vale. 1)how i can connect the new gen. to the old gen. and to the synchronize panel? 2)what is the new gen. to be buy?(rating, etc.) These is my title: To synchronize the generator system of the ____ Hospital. Anyone have a good title? Thanks.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)