The hardware electronic controller you are using has a 1-5
Volt input but the transmitter you use in the field, is a 4
to 20 mA transmitter. So in order for the hardware
controller to accept this input, you install a 250 Ohm
resistor on the controller's input which will convert it to
a 4 to 20mA input.
Weather you need a I/P converter on the control valve
depends on the positioner you will use. The hardware
electronic controller will give a 4 to 20mA signal to the
control valve, so if you want to use a full pneumatic
positioner on the valve, you need to install a I/P converter
and calibrate it for a 4 to 20mA input and a 20 to 100 Kpa
pressure output. You then need to calibrate the pneumatic
positioner for a 20 to 100 Kpa = 0 to 100% stroke.
If you want to use any other type of positioner a I/P will
not be necessary, since in electromechanical positioners the
I/P is already part of the positioner and obviously in SMART
positioners, the input to the positioner is 4 to 20 mA.
Good luck
Is This Answer Correct ? | 24 Yes | 2 No |
Answer / vishal sharma
we need 250 ohm resistane because when we need to opearte
any loop eg.line pressure control loop er need to instal
pressure transmitter in line after control valve on that
time if we instal 250 ohm resistane in controller we dont
have to need another SMPS install for 24v signl to pressure
trasmitter for 2-wire system after install 250 ohm
resistance we recive 24v output trrough controller.
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rohit
A electronics controller needs 4-20mA current and we have
230v or more voltage in industry so to maintain flow of
current 250 ohm resistance is vital.
I=V/R
Is This Answer Correct ? | 2 Yes | 16 No |
what r all the type of viberation measurement measuring in turbin? what's the output of viberation sensor?
what is a vortex flow meter,mass flow meter and electromagnetic flow meter.particular use of this.means in which condition particular meter is used.
If i have 4 Allen Bradely make RS logix 5000 PLC and for viewing that we are using 4 RS view SCADA for 4 different packages. Now, I will want to view two packages on only one SCADA. Then how i will do it?
What is the difference in clamp on type and inline type ultrasonic flow transmitter.
What is the absolute temperature
The process variables that need to monitored and controlled are ________, ________, _________ and
Explain why use mmwc unit?
Please why do we use 4-20ma in instrumentation engineering
How many types of sensor
Difference between ultrasonic flow meter and radar type flow meter
2 Answers Dodsal, Qatar Petroleums,
what is the difference between signal cable and ontrol cable?
When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?