how to tune the closed pid loop?..

Answer / welcome4ujd

Controller Tuning

If the controller is withdrawn from the control panel face,
further adjustments are available which are used to tune
the controller to the process.

When a control loop is commissioned, the controller
settings are adjusted to correspond to those, which have
been specified during the design of the control system. If
a large section of process is to be commissioned; possibly
a mathematical model of the process will have been
developed from which the optimum controller settings can be
calculated for efficient and stable operation. It is these
values which are set into the controller before start-up
and, if calculated correctly, no further adjustment will
be required.

In some cases it will be necessary to tune a controller
without having the benefit of knowing what the settings
should be. It must always be remembered that the
adjustments cover a very wide range of sensitivity and
response. If adjusted haphazardly, the process may shut
down and damage to equipment and lost production may occur.

The task of controller tuning is usually left to an
instrument technician with experience in the cause and
effect of process reaction and controller adjustments.

There are many trial and error methods of controller tuning
which do not involve mathematical analysis and should be
demonstrated by an experienced person, otherwise shutdowns
may occur.

The first adjustment, which would normally be made, would
be to set forward or reverse action as required. A forward
acting controller has increasing output in response to an
increasing measured variable. A reverse acting controller
has decreasing output in response to an increasing measured
variable.
Empirical Tuning Method
Proportional only controller

- With transfer switch at manua1, set PB at maximum
or at safe high value, usually 200% PB.
- Move transfer switch to auto and make changes in
set point. The time required for the disturbance to settle
may then be noted.
- Continue reducing band-width to half its previous
value until the oscillation do not die away, But continue
to be perceptible.
- Now increase the band-width to twice its value.
This gives the required stability, that is, the minimum
stabilising time and minimum offset.

Proportional plus integral action

- Set the Integral Action Time (IAT) to maximum.
- Adjust the proportional band as for a proportional
controller.
- Decrease the IAT in steps, each step being such
that line IAT 1s halved at each adjustment. Below some
critical value, depending upon the lag characteristics of
the process, hunting will occur. This hunting Indicates
that the IAT has been reduced too far.
- Now increase the time to approximately twice this
value to restore the desired stability.

Proportional plus derivative action

- Adjust the Derivative Action Time (DAT) to its
minimum value.
- Adjust the proportional band as described for
proportional controller, but do not increase the band when
hunting occurs.

- Increase the DAT (that is, double each setting) so
that; the hunting caused by the narrow band is eliminated.

- Continue to narrow the band and again increase the
DAT until the hunting is eliminated.
- Repeat previous step until further increase of the
derivative action time fails to eliminate the hunting
introduced by the reduction of the proportional band, or
tends to increase it. This establishes the optimum value
of the DAT and the hunting should be eliminated by
increasing the width of the proportional band slightly.


Proportional plus integral plus derivative action

- Set IAT to a maximum.
- Set DAT to a minimum.
- Adjust the proportional band as for a P + D
controller.
- Adjust derivative using same procedure as for
above, P + D.
- Adjust integral to a related value of the final
derivative setting.

A three-term controller is therefore adjusted as for a P +
D controller and the integral value simply related to the
derivative value.

In many cases, the setting procedure may be shortened by
omitting settings, which are outside the probable range.

The process should then respond to set point or load
changes, where integral action removes offset and the
second overshoot of set point is approximately 1/4 the
amplitude of the first. This is commonly referred to as
the 1/4 decay method and is generally agreed to be the
optimum controller setting for a P + I controller.

The above method is only used when no other controller
setting data is available and must be practised with care.



Optimum Settings (Ultimate Method)

The closed loop or ultimate method involves finding the
point where the system becomes unstable and using this as a
basis to calculate the optimum settings.

The following steps may be used to determine ultimate PB
and period:

1. Switch the controller to automatic.
2. Turn off all integral and derivative action.
3. Set the proportional band to high value and reduce
this value to the point where the system becomes unstable
and oscillates with constant amplitude. Sometimes a small
step change is required to force the system into its
unstable mode. The below figure showing typical response
obtained when determining ultimate proportional band and
ultimate period time.
4. The proportional band that required causing
continuous oscillation is the ultimate value Bu.
5. The ultimate periodic time is Pu.
6. From these two values the optimum setting can be
calculated.





• For proportional action only

PB% = 2 Bu %

• Proportional + Integral

PB% = 2.2 Bu %
Integral action time = Pu / 1.2 minutes/repeat

• Proportional + Integral + Derivative

PB%=1.67Bu
Integral action time = Pu / 2 minutes/repeat
Derivative action = Pu / 8 minutes

Example 1
When a step change was applied to a closed loop system with
a PB% of 14% sustained oscillation of the output was
observed. The time between two adjacent peaks was measured
as 1.2 minutes. Calculate the optimum setting for a P only
& P+I+D system.
[(28%) & (23.38%, 0.6 min/rep, 0.15 min)].

Example 2
A closed loop control system is found to oscillate when the
proportional band is reduced to 23%. A trace on a chart
gives a measurement of 6 mm between adjacent peaks. If the
chart speed of the recorder is 10mm per minute, calculate
the optimum controller settings for P+I+D control.

(38.41%, 0.3 min/rep, 0.08 min)

Is This Answer Correct ?    4 Yes 1 No

how to tune the closed pid loop?..

Answer / kk

if u want tune the controller.
this is compulsory to know process.
first check how much diffrence between SV-PV.
if ur pahese leading then change D value w.r.t time.not
longer time .it should too much smaller.
if ur phase laging then incerease I value.then it will
stablised in 4-5 cycle. cycle time should not be too much
more.
never PV overshoot to SV.
before tuning take the controller in Manual MODE.
in controller put the MV to cotrolled the Process.

Is This Answer Correct ?    3 Yes 0 No

how to tune the closed pid loop?..

Answer / senthil

simple:online tuning.let the system run with no load and
then with low load.
then we can play with the system by varying the
Gain,Integration time, Derivative Gain,Dead band,Tracking value

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is Analog input/output & Digital input/output,

2 Answers   Bapco Bahrain Petroleum Company,


HOW FOREIGN CONTROL SYSTEM CAN BE CONNECTED WITH DCS?

0 Answers  


Why is the length of cable layyed from RTD to temp. Transmitter should be minimum? Why does heating effect takes place in their?

1 Answers   Process Control Technologies,


WHAT IS TSI? HOW ITS WORK

2 Answers  


pt range is -45 psi to 45 psi.friends can you give answer with calculation and with linerity scale like 0%,25%,50%,75%& 100%?

1 Answers   WB,






why 4ma show higher zero ? i have transmiter flow renge 0-1000 m3/h but 4 ma show in monitoring 200 m3/h and 20 ma show 1000 m3/h i want when 4ma show 0 m3/h and 20ma 1000m3/h

3 Answers  


What happens if the Displacer has fallen or has a hole in it?

1 Answers   CCIE,


i am working in thermal power plant . if temperature transmitter is not showing reading in dcs then how can we rectify the problem?

8 Answers   TATA,


Any can guide for QA/QC Inspector in oil & gas region, the procedures, formats standards, design criteria, i search in all enginees but i can't found wat i need?????????

4 Answers   Aramco, Asian Paints,


I am teja. I am studying Msc(tech) Electronics and Instrumentation (3years course) in Andhra university. But my course is not recognised by UGC and AICTE. Please tell me the job opportunities after this course. And i fineshed PLC course in IGIAT ,Vizag.Also complted my short term coure in SCADA, Seimans WinCC in ATI,Hyd.After Msc can i join Mtech for good job? or phd. How i can get good job in INdustrial Automation Side. Please give replay.Because this is my life matter.

0 Answers  


1. what is 3 point calibration & 5 point calibration? 2. If we use hart communicator to set the LRV & URV of a smart transmitter, did we calibrate the transmitter? why? 3. Make a complet list if meterials needed to properly connect a pressure gauge to a steam pipe using 1/2 inch stainless steel tubing. The gauge connections is 1/2 inch NPT-M and the steam pipe tap has a 1/2 inch female coupling, compression fittings are use. 4. What are the tools in loop checking? 5. What would the ISA symbol of a square root extractor look like? 6. What would you do to completely prepare for the configuration? 7. What safety measures must you undertake when doing configuration? 8. what are the two most commonly use programming languages used when we configure a PLC? 9. What would you do if you accidentally skipped a step in the configuration procedure? 10. How would you know if the configuration were sucessful? 11. Name at least 3 selections available when we configure the burnout protection of a controller?

3 Answers   EI Electrotechnical Institute,


which is type of thermocouple is used to measure 1000deg?

9 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)