wil a dc motor run without a starter??
Answers were Sorted based on User's Feedback
Answer / t.suganya
NO
Why starter?
When DC Motor is suddenly connected to a supply source,
it creates stresses on the armature and supply system.
Since at standstill the armature is not developing any back
e.m.f, so the more current than the rated current
and this will cause damage to the motor.
What the starter do ?
A Motor Starter is used for the smooth starting of a motor.
It consists mainly of a variable resistance placed in
series with the armature.
The purpose of this resistance is to restrict the armature
current to a safe value for starting and accelerating.
The other uses of using a Motor Starter is
· To disconnect the motor in case of an overload
· To disconnect the motor when the supply voltage fails
· To disconnect the motor when the field current is reduced
beyond limit.
| Is This Answer Correct ? | 53 Yes | 2 No |
Answer / vignesh
guys we can start the dc motor without starter by using no of resistors in series depending on the rated current
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / senthilnaathan
if the starter is based on increase in resistance can we include some series resistances so as to control the current flow..??
which inturn acts as a starter here??
can this be possible??
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mallikarjuna chowdary
dc mototr doesnt require starter
high starting torques
carbon brushes require to control current
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / thavam
DC motor starting current=starting voltage
for Ex:220 volt= 220 amps
because current limiting used for starters
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / abhishek pandey
without starter we do not start DC Motor
| Is This Answer Correct ? | 3 Yes | 5 No |
How do you select a cable size(cu&Al)for a particular load?
if we convert kw into kva,which one formula use by us,pls tell me?
19 Answers ABB, AEC, BGH,
2.5mva transformer is installed in our company with oltc but it is not working in auto mode ,it is operative in manual mode control wiring is done how can i rectify it?
what is working of communitator in a dc generator?
IF TVM OF TRANSFORMER SHOWS POWER FACTOR ON 33 KV SIDE AS 0.97 LAGGING AND ON 132 KV SIDE IS 0.75 LEADING.IS THIS CORRECT.WHERE IS PROBLEM.
1kva = kw ?
Why effective AC resistance is more than DC resistance of a transmission line?
When batteries are connected in series the voltage increases but the current remains unchanged, how can this be? When you consider ohm's law. i.e. If voltage increases, current increases, providing resistance remains the same.
electromechanical relay type identification example : type=tjmh t-stants for j- m- h-
power requirement of an l.e.d?
Current Transformer's star point must face the protected object for the relay operation?
How will you calaculate the Ct ratio based on connected load 500KVA,and 11KV supply ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)