after syncnhronistion how generator speed controlled by grid
Answers were Sorted based on User's Feedback
Answer / arjunyadav
the generator speed cannot varied ofter synchronisation
because if the speed varies then the frequency varies if we
change the speed then the over or under frequency relay
will operate and trips the circuite.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
The grid is more powerful than the generator or the
station.The speed of any generator is decided by the grid
while synchronizing or running.3 % variation in frequency is
allowed as per IE rules.
Is This Answer Correct ? | 2 Yes | 1 No |
The generator is magnetically coupled to the grid
frequency. If the fuel to the generator is increased the
generator will try to increase speed but as it is
magnetically locked to the frequency it will take more load
instead. The reverse will happen if the fuel is decreased.
Under some circumstances the magnetic coupling can be
broken. If this happens the energy from the grid will try
to drive the generator back into synch. This can cause
extensive damage to the generator and/or switchgear.
Therefore protection should be used to stop this from
happening.
Is This Answer Correct ? | 0 Yes | 0 No |
Explain how you intend to work under pressure to meet up with deadline target?
If a fan get trip and run in reverse direction due to system flow. Now in this condition during starting how can a VFD bring this negative speed to zero and later run in forward direction?
2 Answers Aditya Birla, Siemens,
take 100kva DTR( delta/wye ), what ll happen if we connect 11kv to LT side instead of connecting to HT side? will the DTR behave as a step up transformer or something else????
waht is the working principle of saft starter & what is the difference in vfd & saft starter
What type of wiring series or parallel is used for conventional and addressable type FAS & why?
Why generation voltage in thermal power plant is between 11kv to 33kv?
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
What is the main difference between generator and alternator
How to decide and select the different earthing wire size for the different types of earthing
WHEN THESE TRANSFORMERS WINDINS CONFIGURATION ARE USED? SPECIALLY EXPLAIN REGARDING STEP UP AND STEP DOWN KEEPING IN MIND.AND REGARDING LOAD ALSO. a.star to delta b.delta to star c.delta to delta d.star to star ALSO EXPLAIN WHY V USE 415/415 TRANSFORMERS IN TUBEWELLS?
We are designer please help me calculate the size of 11kv cables from step up transformer to M.V panel, total load is 5 mega watt distance 900 feet (used aluminum type cables) please provided formula for calculate the cable with example.
how we can convert 3 phase to single phase without using any transformer