what is the use of vector group in transformer. means what r
the application of various vector groups?
Answers were Sorted based on User's Feedback
Answer / iamdon
Vector groups are used to indicate the phase difference
between primary and secondary quanrtity in case of 3 phase
transformers.
Application:
On the basis of vector group, we choose the transformers
which could be operated in parallel.
Two transformer belonging to same parallel group can be
paralled only.
phase difference for various group
Group 1= 0 degree.
Group 2= 180 degree.
Group 3= -30 degree.
Group 4= +30 degree.
Depending upon the applications Star,delta or ZigZag connection
is used.Also there are many possible winding pattern even for
same connection pairs(e.g. star/delta, delta/star, delta/delta,
star/star, delta/zigzag etc).So we have inherent phase
difference with respect to each other.This difference is
technically represented by different notations.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / alpesh c
hey thanks for the answer but still i am having question
that y so many groups? y to alter connections for various
group? what are the effects of such connections ? cant we
use only dy11 everywhere? is there any particular
application for each group?
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gajendra pal singh
Yes vector group are used to indicate the winding connections
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rakesh
To identify the HV & LV Side as well as the phase difference between primary & secondary voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / paul
By having multiply vector groups, you have the ability to parallel 2 or more transformers with with different vector groups by altering their connections.
EG. you can change a Yd11 into a Yd1 by changing the HV and LV phase sequence from positive to negative.
So with that in mind a Yd1 can be converted to a Yd5 if required by placing L1 onto L2, L2 onto L3 and L3 onto L1. The reason for the 4 vector group shift is down the fact that you have rotated each phase by 120 degrees
| Is This Answer Correct ? | 0 Yes | 3 No |
When we have earthing mesh or underground earthing network in industrial plants, weather we have NT-S or NT-C-S kind of earthing system, so eventually weather we must use 4 or 5 wire in 400 volt level (For example 3×150+70 mm2 or 5×150 mm2) in this connection I would like to know exactly the paragraph of IEC or IEEE number
what is mean by PID & Principal of working
why star point of motor shall not be grounded?
why motor burns ?
in parallel operation of power transformer why the distance between power transformer and capacitor bank feeder is necessary to know
Waht will happened if reactive power increase in the line? waht about active power increase too?
How we can determine short circuiting current any plant and for example a plant which power generation is 415 volts and plant load is 500 kw.
why generator efficiency is more in swinburnes test?
15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ? and what will be per phase current for 15 kva
Why two nos. un-tensioned wires are placed inside the PSC poles used by powergrid in RGGVY works.
how many types are their in switchyard or substation(like D,I TYPE), what is differant between them
Hi, My question is our total motor load is 55 kw.so what cable size required for main supply. Please reply
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)