What is an analog input - output , digital input - output .
Any example ???? How they r known its ai-ao or di - do
Answers were Sorted based on User's Feedback
Answer / barok
AI- means input of 4-20mA comes from transmitter to DCS
AO- means output of 4-20mA comes from the controller on DCS
DI- means input of 0 and 1 comes from switch to DCS
DO- means output of 24VDC come from DCS going to solenoid.
Is This Answer Correct ? | 47 Yes | 8 No |
EX. DI like sensor.limit switch and bush bottom
DO like to run for example motor
for contactor or relay or solnid valve
AI like level transmitter or pressuer transmitter TC
AO like control valve
Is This Answer Correct ? | 22 Yes | 0 No |
Answer / sudarshan sankapal
AI means field genarated signals comeing to Dcs or PLCs by the use of 24v DC suppy... ex sensors
AO means DCs or PLC genarated or field genarated signals going to control process parameters...ex control valves input 4 to 20ma
DI its logic signal 0 or 1 state came from electrical VFD drives or field...
DO its logic signal genarated in DCs to control feild process parameters..ex solenoid valves
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / mayursinh amw
A0 means analog voltmeter, supply come from AO cardto volt
meter
Is This Answer Correct ? | 3 Yes | 13 No |
how many type conductivity sensor ?
cascade controller is feed back or feed forward or both
I am using 971 Enraf radar level transmitter for LPG tanks ,the tank side indicator gives the error code 999999999FL can any body give me any diagnostic for this issue?
INtools Trainining
1 Answers Monarch Techno Engineering Solutions,
how the flow rate is measured from a pipe with the help of pressure?
what is the function of a zener diode ?
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
what are the levels of automation?
what is full form of SMART
46 Answers Infosys, ITC Infotech, Lanco, Rosemount, Solvay,
Explain the working principle of lvdt?
I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?
how many types of thermocouple cable are? give the name of each type.