Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


when the operation engineer told you that he gives the
control valve order to open but there is no response !
what will you do ?
and if you found that there is astuck , what will you do ?
(note : it is apanumatic valve )

Answers were Sorted based on User's Feedback



when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / chitturi bhaskara rao

1.First measure 4-20mA in field side if cannot get 4-20
then check AO card , if u got 4-20 in field side then check
positioner ,
2. make sure thatt sufficent air supply i,e 3 to 4 bar at
inlet of positinoer.
3.If all correct still valve nvr moves then remove
positionner from the valve and supply the air directly to
actuator ( to 4 bar max) then valve moves smoothly then
check angle of postioner while ur fixing positoner on
control valve .
4 if valve nvr moves smoothly means in side valve jam need
to send over haul

Is This Answer Correct ?    20 Yes 0 No

when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / maneesh

after doing all the priliminary inspection if u found the
valve is struck, u can directly give the air supply to the
actuator not:direct applying og air supply may diamage the
valve it should be done with sufficiant care.if the struck
is minor by repeaded giving of supply air will slowly
remove the struck.agfer this still its struck u can remove
the valve from the praocess line and chel the valve body
whether any solid material bloks the way.if that u can
clean and fix it back

Is This Answer Correct ?    2 Yes 0 No

when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / b.kumaran

after doing all the priliminary inspection if u found the
valve is struck, u can directly give the air supply to the
actuator in a repeated manner.if the struck
is minor by repeaded giving of supply air will slowly
remove the struck.still its struck then loosen the body
bolts and try to open by the above method. If still there is
a struck up then u can remove the valve from the process
line, dismantle and clean the valve body whether any solid
material bloks the way.

Is This Answer Correct ?    0 Yes 0 No

when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / 808

Simulate 4-20mA it with a DMM at control valve. If it works
there, then check wiring.

Is This Answer Correct ?    1 Yes 3 No

when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / aatif alvi

check if the proper volatage i.e 4-20ma is changing the the
operation engineer changes he valve position. if it is
changing the the problems might be with the solonoid..some
times moving the solinoid with screw driver makes it work
again,, as it got stuck due to rusting.

Is This Answer Correct ?    1 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

why pressure 3-15psi is used as industrial standard and what is the reason

2 Answers   JAL International, UltraTech,


Why does a pressure gauge installed on reactor, doesn't have any vent line below to release the pressure? Is it any kind of designing mistake or it actually does not require any vent line? And if it does not require any vent line below it then how we are gonna release the pressure built inside the pressure gauge?

0 Answers   Process Control Technologies,


How to erection of DCS Panel at site step by step

0 Answers  


I have 0.75mm sq multicore cable (IS type) , can use instead of same type but 1.5 sq mm cable ? Note : The distance is around about 150 meter.

0 Answers  


What is force balance principle? State some of its’ advantages.

0 Answers  


What is SCR?

9 Answers  


I want to install analog type, flange mounted gas flow meter (line size - 2"), for CNG flow measurement.Kindly give some details of flowmeter or suppler name, available in India.

1 Answers  


How to calibration a control valve?

0 Answers  


Define all the process Variable and state their unit of measurement. ?

0 Answers  


why direct mounted pressure transmitters is always installed with DBB ( double bleed block) valve in process line or top of the tanks ?

0 Answers  


where can i find a flameproof hmi unit?

1 Answers  


what is the field bus calble ? what are diffrences in orang colur cable and black coular calble ?

0 Answers   ABB, Yokogawa,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)