If 440 V supply has given at the secondary winding of
transformer at that time if we apply 11 KV at primery then
what will happen???????
Answers were Sorted based on User's Feedback
Answer / s c budhiraja
nothing will happen if rated voltage is applied to both the
windings
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / parin
if transformer ratio is 11000/440,and supply is given according to polarity with same power factor then no power flow in sec. so it not damage transformer but if polarity not correct then two emf addition gives high current like s.c.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kalidass
Well Mr. Buthiraja,U r correct Bcoz in our plant also we
are using 110(Primary)/6.6 Kv(Secondary)Transformer..But We
exported the power to grid through 6.6 Kv side itself...
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ratnagiri
Source should not be given from both the sides. There will
be a severe S.C Fault and the transformer will be damaged.
| Is This Answer Correct ? | 0 Yes | 3 No |
what is the pressure in side transformer under normal condition?
what kinds of Transformer oil grade is better for power transformer ?
Can anyone explain the power flow in flouresent lamps (tube lights) .What are the functions of Starter & choke used there?
in 3-phase transformer which type of transformet is used in output side?
the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?
why maintenance batteries used in DG sets not in MAintenance free Batteries.
Where voltage are high and current to be interrupted is low the breaker preferred is:
what is difference between earth fault& restricted earth fault.
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
the inertia constants of two machines are respectively 30and 42 MJ per MVA.when the change in frequency due to change in load in first machine is 12 Hz,the change in second machine frequency will be?
what is the Space heater? why using in Electrical motor?
what is derating?, why it is neccesary, it is same for all means for drives, motors,and cables.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)