Answer / iamdon
Yes.
A transformer designed for a particular voltage and
frequency rating can be used for different set of
mentioned ratings as long as ratio of voltage to the
frequency does not deviates from designed value.
By emposing this constraint, the core of the transformer
will not saturate.Since the winding is assumed capable of
sustaining overheat, so only deciding factor is V/f ratio.
i.e,(V/f)=fixed at rated value.
50 Hz at 500V
25 Hz at 250V
75 Hz at 750V and so on.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 8 Yes | 0 No |
What must be the minimum distance maintained between 2 Generators as per International standards?
Determine the MVA rating of the power transformer given that 110/66 kV,1000 Amps. Folks how can i calculate the MVA rating with this Data??Plz Help........
in 31.5 mva power transformer how to set of wti and oti?
The DC current waveform is - . What about the fire alarm waveform?
How to make vector group test of transformer?
Why is reating of t/f in kva but for inverter in kw ?
I am an electrical power engineer and arranged power system for a data center, I installed MCB, ELCB and erthing system TN-C-S. But some times several ELCBs Disconnect circuits at the same time! what may be the reason? (the ELCBs are 25A ,30mA)
how freewheeling diode improves the powerfactor
how to test power transformer.YNd11
how to claculate the ups load in KVA pls give the if any fourmoul?
We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).
Is earthing done for AC or DC or both?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)