Answer / larry gremillion
To set the zero trim for K-TEK (a member of the ABB group) Foundation Fieldbus level devices:
1. In the Transducer Block enter the following – exactly as typed – into the CONFIG_ACCESS field:
KTEKFACTORY
Write the change to the device. This will change the GENERAL_STATUS field to ‘Access Factory’ before changes can be made and saved.
2. Move the float on the probe to the lowest position. This point is TRIM_POINT_LO.
3. Set the CONFIG_VALUE to the level value (in inches) of the lowest float position (typically 0”). In the CONFIG_METHOD field of the transducer block select TRIM_POINT_LO from the pull-down menu. Write the changes to the device. When the value in the TRIM_COUNT_LO field changes to match the value in the SENSOR_RAW_LEVEL_1 field the change has been saved.
4. Exit ‘Factory Access’ mode by typing a minus sign into the CONFIG_ACCESS field and write to the device, or by cycling power to the device. This completes the sensor trim procedure for K-TEK Foundation Fieldbus level transmitters.
7. Manually copy all settings and values from SENSOR_RANGE in the Transducer Block to the XD_SCALE in the AI Block (CH 1). When these data are written to the device they will automatically be copied into the relevant parameters in the Transducer Block.
I hope this helps!
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ram nath singh
first I will go to (Hart application-on line application-device setup-diag/ service-calibration-sencer trim) I can choos zero trim for T Tx.
| Is This Answer Correct ? | 2 Yes | 2 No |
i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500 ltr/hr.) what should i do?
How to check loadcell working or notworking
Can any one send me IOCL instrumentation question papers.. i dont know the pattern of the questions and what to prepare can any one help me on this .. my email id is anwarnishil@gmail.com
Wht is Dry Leg Calibration and Wet Leg Calibration?
What is the difference between DCS and SCADA?
why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .
1 Answers Flour Tech Engineers (P) Ltd,
What is difference between “Fault Tolerant” & “Fault avoidance” PLC? Application where these system s are used?
tell me about Woodward505 Function as a point of Instrument Engineer.
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
How will you select suitable Instrument for Process line/Tank/Vessel?
Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?
What is the use of valve positioner?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)