How to zero trim the level transmitter by using foundation fieldbus communicator.
Answers were Sorted based on User's Feedback
Answer / larry gremillion
To set the zero trim for K-TEK (a member of the ABB group) Foundation Fieldbus level devices:
1. In the Transducer Block enter the following – exactly as typed – into the CONFIG_ACCESS field:
KTEKFACTORY
Write the change to the device. This will change the GENERAL_STATUS field to ‘Access Factory’ before changes can be made and saved.
2. Move the float on the probe to the lowest position. This point is TRIM_POINT_LO.
3. Set the CONFIG_VALUE to the level value (in inches) of the lowest float position (typically 0”). In the CONFIG_METHOD field of the transducer block select TRIM_POINT_LO from the pull-down menu. Write the changes to the device. When the value in the TRIM_COUNT_LO field changes to match the value in the SENSOR_RAW_LEVEL_1 field the change has been saved.
4. Exit ‘Factory Access’ mode by typing a minus sign into the CONFIG_ACCESS field and write to the device, or by cycling power to the device. This completes the sensor trim procedure for K-TEK Foundation Fieldbus level transmitters.
7. Manually copy all settings and values from SENSOR_RANGE in the Transducer Block to the XD_SCALE in the AI Block (CH 1). When these data are written to the device they will automatically be copied into the relevant parameters in the Transducer Block.
I hope this helps!
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ram nath singh
first I will go to (Hart application-on line application-device setup-diag/ service-calibration-sencer trim) I can choos zero trim for T Tx.
| Is This Answer Correct ? | 2 Yes | 2 No |
what is 24vdc live and dry supply
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used? Please tell me its Calculation formula.
please suggest me, how can i change the display setting in term of unit in place of % of Honeywell pressure transmitter ST3000S100?
in the boiler in the main steam line and its bypass line and the startup vent vales are only motorised valves why cant we use other types of valves such as pneumatic.
what is all types of analyzer in water production plant?
what is the input of conductivity sensor and meter during the calibration time and what is the output?
How to set up the various advanced process controllers, input the proper parameters, and tune those controllers given related control system information.
units for vibration in power plant
1)why we are using mostly Ultrasonic Flow meters to measure flow, rather than Radar waves? 2)why we are using Ultrasonic waves and Radar waves to measure the Level?
What is the difference between HMI and SCADA?
how the transmitter send MA?
Can I route 110 VDC and 24 VDC in a same Duct for our Interposing relay cabinet? IF yes or NO Please provide me IEEE Std. for the same. Please i required it on Urgent basis, i need to design IRP Cabinets and we have MCC 110VDC and Our Coil side is 24VDC, Please help as soon as possible.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)