Answer / larry gremillion
To set the zero trim for K-TEK (a member of the ABB group) Foundation Fieldbus level devices:
1. In the Transducer Block enter the following – exactly as typed – into the CONFIG_ACCESS field:
KTEKFACTORY
Write the change to the device. This will change the GENERAL_STATUS field to ‘Access Factory’ before changes can be made and saved.
2. Move the float on the probe to the lowest position. This point is TRIM_POINT_LO.
3. Set the CONFIG_VALUE to the level value (in inches) of the lowest float position (typically 0”). In the CONFIG_METHOD field of the transducer block select TRIM_POINT_LO from the pull-down menu. Write the changes to the device. When the value in the TRIM_COUNT_LO field changes to match the value in the SENSOR_RAW_LEVEL_1 field the change has been saved.
4. Exit ‘Factory Access’ mode by typing a minus sign into the CONFIG_ACCESS field and write to the device, or by cycling power to the device. This completes the sensor trim procedure for K-TEK Foundation Fieldbus level transmitters.
7. Manually copy all settings and values from SENSOR_RANGE in the Transducer Block to the XD_SCALE in the AI Block (CH 1). When these data are written to the device they will automatically be copied into the relevant parameters in the Transducer Block.
I hope this helps!
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ram nath singh
first I will go to (Hart application-on line application-device setup-diag/ service-calibration-sencer trim) I can choos zero trim for T Tx.
| Is This Answer Correct ? | 2 Yes | 2 No |
Boolean algebra
I want measure the volumetric flow of gas in waste heat recovery Boiler?Tell me how and which type of instruments required. Plz mail me:naba02222@gmail.com Sam please post the answer .
what is the imbustion control loop
what is loop1 and loop2 in MTS LT?
Can anybody explain about wellhead control system.
one rtd sensor which is connected at middle of distillation column where actual temp. is 100deg but when we tight this sensor at thermowell end it goes down to 90 deg & when remove from the thermowell(but sensor end dipped in well) showing actual reading, what is reason?
please send the drdo exam paper
How to check range of DP Transmitter
What is Modbus communication
If the vibration probe near to the shaft,then output voltage will be decreased r increased?How?
What the basic of communication?
what's meanning of 1250KVA and how to calculate with Volttage and Current. answer give with example.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)