where we are used split range control
Answer / deepan.p
split range control means we have only one measurement &more
than one manipulated variable.
ex:
seal steam system of turbine &turbine driven boiler feed
pump.
description
aim of system is to maintain seal steam pressure constant.
it has two control valves name it as seal steam valve&leak
off valve.
upto (4-12)ma(3-9)psi seal steam valve operates
ex:
if its closed for 4 ma its fully open when it receives a
commend signal of 12ma.
after that (12.1-20)ma(9-15)psi leak off valve operated.
ex:
normally it'a fully open at 12ma .if commend reaches 20ma
the valve will be closed .
that what they designed the control system and field control
valve positioner.
| Is This Answer Correct ? | 9 Yes | 2 No |
what is isolation Transformer???...
what are the on/off valve precaution?
Hi friends, from Aug 4th onwards iam getting spikes for analog inputs in our DCS for a period of 800ms. I throughly checked every thing, finally i found that the DI, DO's from MCC panels shields are terminated in the Signal Earth where Analog Input signals shields are terminated. Is there any problem with this type of termination?. i checked the induction voltage from MCC and getting around 25VAC, please suggest me in this concern. Our plant is 8months old only. DCS is Siemens Make Simatic PCS7, and the transmitters are Yokogawa make.
how to calibrate the interface leveltrol
How you calibrate absolute pressure with the calibration range of 0 to 1000 0C Absolute. Please explain the procedure for calibration.
Any can guide for QA/QC Inspector in oil & gas region, the procedures, formats standards, design criteria, i search in all enginees but i can't found wat i need?????????
4 Answers Aramco, Asian Paints,
what is vfd(variable frequency drive)?type of vfd.
how will you check torque value during Factory acceptance Test for control valve/ESD ON/OFF VALE how will you confirm this torque value is being correct, Which document will you be refer.
where can i find a flameproof hmi unit?
i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....
Briefly describe instrumentation job
what are the problem's will accure in dcs or plc hadware and what are the solution for it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)