how can you set a zero and span of transmitter?
Answer / bunny
First give the LRV(Lower Range Value)to the transmitter.If
it is an electronic transmitter,the o/p should be 4mA.If it
is a pneumatic transmitter,the o/p should be 3psi.If we are
not getting the above values,adjust the zero screw in the
transmitter by a screw driver,till we are getting 4mA or
3psi.This is called zero adjustment.Simillarly give URV
(Upper Range Value) to the transmitter.So the output for
electronic and pneumatic transmitters should be 20mA and
15psi respectively.If we are not getting it,adjust the span
screw in the transmitter by a screw driver till we are
getting 20mA or 15psi.This is called span adjustment.
LRV & URV:Suppose the range of a transmiter is 0-30psi.Then
LRV=0psi & URV=30psi.
| Is This Answer Correct ? | 23 Yes | 0 No |
how to commission furnace ( water heater)
what is radar type level transmitters and its basic principle and how to calibrate it
why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .
1 Answers Flour Tech Engineers (P) Ltd,
hi... i'm about to learn siemens plc i came across following question in my mind ... plr ans 1. hw motor operated by plc 2. hw drive operated by plc explain dis by both ladder logic diagram and hardware config , connection
there are two candidates p and q in an election.During the campaign,40% of the voters promised to vote for P ,and rest for Q.however, on the day of election 15% of the voter went back on their promise to vote for P and instead voted for Q. 25% of the voters went back on their promise to vote for Q and instead voted for P.suppose,P lost by two votes,then what was the total no. of voters.
components of control circuit belongs to control valve
What is instrumentation control?
I have observed in field instrumentation work... I remove the fuse of an analog transmitter then it shows 7.75 kg/sq cm (which is practically wrong value)in DCS and when put the fuse it shows 0 in dcs. Then cheach the field transmitter termination and found moister. clean that and then it shows 1.1 kg/ sq cm which is right value. Please describe the above phenomenon.
how can we tune a PID. If it is by zeiger nichols method..please explain briefly with help of an example.
what is electric motorised valve working principle.
what is control valve and how is work
How earthing can be checked????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)