Answer / bunny

First give the LRV(Lower Range Value)to the transmitter.If
it is an electronic transmitter,the o/p should be 4mA.If it
is a pneumatic transmitter,the o/p should be 3psi.If we are
not getting the above values,adjust the zero screw in the
transmitter by a screw driver,till we are getting 4mA or
3psi.This is called zero adjustment.Simillarly give URV
(Upper Range Value) to the transmitter.So the output for
electronic and pneumatic transmitters should be 20mA and
15psi respectively.If we are not getting it,adjust the span
screw in the transmitter by a screw driver till we are
getting 20mA or 15psi.This is called span adjustment.
LRV & URV:Suppose the range of a transmiter is 0-30psi.Then
LRV=0psi & URV=30psi.

Is This Answer Correct ?    23 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Which buffer solution is used for PH transmitter calibration?

3 Answers  


Reason for capillary type dp level transmitter fluctuation

0 Answers   BMB, Enppi,


installation process of orifice,a question asked for confusion creation in interview by BARC 1.if orifice is tightly fitted with pipe ,it will act like venturi 2.if orifice is left hanging in between liquid it will not create the pressure difference exactly,

0 Answers   BARC,


difference between repeatability and reproductability

1 Answers   IOCL,


Explain Difference between Bech set and operating range of control valve

3 Answers  






What is the difference between sdv and bdv ?

1 Answers  


Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.

3 Answers   HPCL,


Difine flashing , Cavitaion & Noise? how to minimize these effects

3 Answers   L&T,


What is the difference between pt100, pt500 and pt1000 RTDs?

3 Answers   ICI Pakistan,


control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also good condition & incoming inst air line also constant pr.kindly give us correct answer?

5 Answers   Madhu Power,


If mVolts can drop by resistance of wire as compare to mA, then how thermocouple mV reaches in CCR as accurate value?

7 Answers  


how can i communicate with non-national instruments device with pc via labVIEW8.2

3 Answers   Google, Mico, National Instruments,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)