I have a steam flow DP transmitter that has output
swinging. Steam valve is in manual.I have good steam
pressure. The impulse lines have steam tracing on them. The
steam tracing has a hole in it that is blowing raw steam on
the high side impulse line only. Could this be causing the
swinging?
Answer / carl_ellis
Answer:
Yes, live steam on an impulse line could cause pressure swings.
Blowing live steam on an impulse line could conceivably heat
the condensate in the impulse tubing enough to boil it.
Even if it doesn't boil, a deadheaded impulse line with have
thermal syphon flow occuring as the hot spot condensate
rises and its place is taken by cooler condensate.
If boiling is occurring, then it could be intermittent
boiling with associated pressure pulses: as the steam
bubble(s) move away from the hot spot and cooler condensate
takes it place.
None of which should be happening in an impulse line.
The high side is 'seeing' these artifacts as forces on its
diaphragm which is creating pressure swings.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
FOR CO/CO2/O2/NOX applications which of the following manufature is best? and what is the basic principle of gas analysers? ABB/YOKOGAWA/EMERSON/SIEMENS/TELEDYNE/THERMOFISHER
plz you help about Que paper of mahagenco previous your,any model paper relad to it{maharastra power genration}
How to Calibrate Flow Switch in field
what is dc moter.
0 Answers Jindal Steel and Power, Lupin,
calibration of instruments.
Single acting ON-OFF valve. it is air to open. when sov energized , valve will be open, so during that if air fail then what will be the condition of valve ( open or close ) ???
why the derivative in PID is always set to zero?
what are the documentation and instrument identification system used to identify the correct device to be calibrated? name atleast three.
what is cavitation ?
how can i calibrate the temperatuture gauge used by temperature bath(dry block) i mean step by step procedure?
What types of Instrumentation Related Questions can an Interviewer ask in a Telephonic Interview ?
What is the calibration procedure of Drum level transmitter if range is 0 to -400 mmh2o in lab?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)