Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calibrate a control valve?

Answers were Sorted based on User's Feedback



how to calibrate a control valve?..

Answer / k.thirunathan

calibration instrument required.
1.portable pneumatic calibrator
INPUT signal OUTPUT
Generate 0.2 kg/cm 0% of v/v travel
0.4 25%
0.6 50%

0.8 75%
1.0 100%

If you observe any deviation adjust accordingly.

Is This Answer Correct ?    137 Yes 30 No

how to calibrate a control valve?..

Answer / deba

BY using DRUG calibrater we can easily calibrate just we
need a air line having pressure of 6kg as input of CV.
by giving 4-20mA signal through DRUG.
for example
4mA CV in close position
8mA 25%
12mA 50%
16mA 75%
20mA 100%

Is This Answer Correct ?    123 Yes 21 No

how to calibrate a control valve?..

Answer / azmat

To calibrate a valve first check the input signal range if
it is 0.2 to 1.0 Kg/cm2 or different.
Calculate the span ( Difference between higher limit to
lower limit=1.0-0.2=.8 ) Now divide it in four equal parts
that is 0.2 Kg/cm2 this is 25% of the span.
Now check the valve travel like 2 inches, 3 inches or any
other value Divide it in four equal parts 25% of the travel.
Apply 25% of the span value+ 0.2= 0.4 Kg/cm2 it is 25% of
travel and apply full span value and see you get the
complete travel if you find difference adjust the spring
accordingly.

Is This Answer Correct ?    82 Yes 10 No

how to calibrate a control valve?..

Answer / venkat

before do the stroke checking we have make sure the bench
calibration after that we should check 0-100% stroke

Is This Answer Correct ?    77 Yes 18 No

how to calibrate a control valve?..

Answer / jayesh

If the valve is SMART now we can use a HART communicator to calibrate the control valve.Give the supply pressure according to the valve name plate then use HART communicator and give 0% 25% 50% 75% & 100% check the travelling of valve

Is This Answer Correct ?    52 Yes 12 No

how to calibrate a control valve?..

Answer / shefeek salim

In Control valve Calibration,its of two types;
1.Stroke Calibration
2.I/P Converter Calibration
1.Stroke Calibration
it means for the movement (opening and Closing) measurement of stroke through the Scale,from 0 to 100 percentage of valve Closing/Opening,according to the standard air pressure supply or milli amps supply(3 to 15 psi,4 to 20 mA)
2.I/P Converter Calibrtion
It is comparatively simple one,but it can be done in two ways,
2.1 Simulate the std 4 to 20 mA as input Check the output from the I/P
2.2 Simulate the std 4 to 20 mA to the I/P converter as input and measure the Control valve stroke movement through the scale(0 to 100%)

Is This Answer Correct ?    25 Yes 0 No

how to calibrate a control valve?..

Answer / c.grema@yahoo.com

first you have to now your limits if its pneumatic work
from 20 to 100kpa if current i 4 to 20ma
supply pressure,
1.bench set
2.beam alignments
3.calibration

Is This Answer Correct ?    30 Yes 6 No

Post New Answer

More Instrumentation Interview Questions

if we have 380 KVA DG. how to calculate Power Factor. With detailed formula

1 Answers  


Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?

2 Answers  


How to Calibrate Radar Level Transmitter in Field

0 Answers  


why we are not using the turbine flow meter in the steam service?

0 Answers   Jaypee,


What is shriking and swell effect for a boiler ?

1 Answers  


Is it possible to drill additional gland hole in EExd or EExe JBs? What are the points to take care?

2 Answers  


why the positioner output is 3-15psi

5 Answers  


can someone tell me about electronic speed switch &how it conect with proximittyswitch?(with dgm)

0 Answers  


Witch type cable use for rtd ,why?

2 Answers   Sugar Factory,


Q- Which of the following is Close loop system - a-)respiratory System b-)traffic light system c-)washing machine d-)Room heater my option is A, what is our take on option B & C

4 Answers   Sail,


meaning of SMART

3 Answers   ISRO,


what is ment by PID controllers? explain with example?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)