if 1hp jet motar drop voltage when start from 220v to 120v give the reason and solution.
Answer / k.prakashchandra
It may be due to voltage drop in the line.Momentary drop
while starting only, can be ignored.Connect a load of about
500W and check for voltage drop.If the drop persists then
examine for loose connection/joint which could be any where
from dist transformer to the point of measurement .If you
don't detect any fault still, test the motor.Voltage between
neutral and the earth indicates a loose joint in the neutral.
Is This Answer Correct ? | 1 Yes | 0 No |
Voltage drop is the:(a) Maximum potential(b) Difference in potential between two points(c) Voltage at the end of a circuit(d) Voltage produced by a source
what is the function of Choke?
9 Answers Airport Electrical, Cummins, Tamco,
What is the formula to calculate the no load current of a single & three phase induction motor
What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel which contain VCB? In which standard i shall get this information.
what is die electric strnth of transformer ?
what is power factor
What is the difference between Surge protection device and Lighting arrester?
what kind of motors are used in the winders of coal field?and what are the various methods of it's speed control?
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
0 Answers Alka Electromech, Aramco,
Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem
at high temperature conductivity increases for conductor what will happen for long transmission when temperature is high?
How would u describe the function of a generator & motor?