Is it advisable to buy a plot for house construction near
High Tension Power lines? If it so how much distance it
should be away from power line? Iam residing at Chennai,
Tamilnadu, India.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
If you are able to furnish the voltage ,the clearances can
be supplied. Ascertain the voltage and contact the Govt
electrical inspectorate of your area to know about
clearances to be maintained as per IE Rules.Or you can buy
the rules book in the market.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / k.prakashchandra
For buildings,as per 80 of IE Rules 1956,the vertical
clearance for high voltages upto 33000 V is 3.7 m and for
EHT 3.7 m +0.3 m for additional 33000 v or part
thereof.Horizontal clearance - for 11 KV 1.2 m, 33000V -2m
and for EHT 2m + 0.3 m for additional 33000 V or part thereof.
Is This Answer Correct ? | 5 Yes | 3 No |
Getting nusense tripping in a 11KV soft starter, have checked all it control supply & contactors but did not get any fault please help.
How i can calculate the cable size for given load,there is any formula,for 3 phase and single phase
2 Answers Prescient Technologies,
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?
how to varied the frequency in transmission line and how i kept it as a constant one?
Please nybody say, weather the result of Bharat Oman is declared or not? Probable date of declare???????
Differences between 415v ac and 440v ac
how encoder works?
How many Cylinders are there in Diesel Generator?
Sir we are using 250 kva DG its Diesel consumption 25 lits / hrs maximum load 160 kva now how to calculate units/ litres
Why we get neutral from EB department, if not what will happen if we use earth instead of neutral? what is the result at the time of monsoon or rain with thunder and lighting ?
maintenance parameters of sewage treatment plant
How size of Earth Strip is determined for a particular Fault current.