Getting nusense tripping in a 11KV soft starter, have
checked all it control supply & contactors but did not get
any fault please help.
Answers were Sorted based on User's Feedback
Answer / arun
Check your load.Check the relay settings and current
measured during starting.
Check winding resistances in each phase,earthings,IR values
of the motor.
Run the motor without load for sometime if possible monitor
the current in each phase.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / neeraj katoch
check the motor on no load , check the winding of motor and
check the cantrol panel of motor may be realy upset.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why neutral is used in electrical system?
What is EHT tariff or Power factor Tariff ????
What device is use for metering current at lt consumer end..??
For RCD (Residual current device) Icu is defined. How i can find Ics for them?
Power Factor Correction Panel (Manual & Automatic)
why we measure ouput of transformers in kva.
why we are using earth pit in sub stations.?
What is DC series motor?
what is phase and neutral.
I have 12MW gas engine based power plant its running parallel with grid. my problem is When cpp run in island mode(without geb) that time geb transformer power factor is 0.2 lagging. When cpp run with parallel that time power factor is 0.94 lagging So how can i maintain power factor ofgeb transformer in island mode 0.9 lagging?
Why armour HT XLPE power cable required to Earth?
What is excitation in case of dc motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)