Why we get neutral from EB department, if not what will
happen if we use earth instead of neutral?
what is the result at the time of monsoon or rain with
thunder and lighting ?
Answer / kiranganesh
1 because to get back the utilized current.If we used earth
as a neutral point than meter will not rotate I mean it will
not measures our use power and it is the best path to get back
supply where as earth is not in uniform like neutral point in
rainy season there are lot of chances of shock to us so EB
dept gives a neutral point to us.
kiran.sugandhi@yahoo.in
Is This Answer Correct ? | 1 Yes | 0 No |
when we use neutral line as grounding.
what is SWA type of cable?????
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
why we short ckt the secondry vo5tage/ winding in transfr and motor?
For what purpose an AVR in generator sensing generator output voltage?and how the sensing is done by AVR?
Can anybody tell abt concrete encased earthing or grounding?
What is the problem, if a circuit breaker is not closing.
What is relation between mu(nought) and epsilon(nought)?
A cable with concentric PE conductor must be used with frequency converter circuits what does its means.?
where we use stardelta starter and dol starter
what is the difference between a feeder and a cable?
Transmission line design. Say, I have a 1MVA generator and 2 transformers that will have the same load. What would be the proper rating of the trasformers? Is it safe to say, that I will simply divide the total rating of the generator?