I have a 3 phase 600 volt prim. feed and a 120/208 sec.
Isolateing tranformer .We are using this system for safety
against shock . What is the proper grounding ?? Does the
common on sec. get earth ground ???
Answer / k.prakashchandra
You are using isolating tr for isolating earth to avoid
shock .Then,why do you want connect the neutral of secondary
to earth ? The very purpose is defeated.
Is This Answer Correct ? | 0 Yes | 0 No |