where HT & LT capacitor uses ?
Answers were Sorted based on User's Feedback
Answer / maprayil
Capacitors are of many types, viz, power capacitors, energy
storage capacitors, microfarad capacitors, surge protection
capacitors etc. From your question, it appears that you
are referring to Power Capacitor. LT capacitors are used
in single phase (230V) or 3 phase (415V) system for
reactive power compensation where the loads are inductive
in nature. As far as HT capacitors are concerned, this can
be of any voltage denomination viz., 11 KV, 22 KV, 33 KV,
66 KV, 132 KV, 400 KV etc. Generally these type of
capacitors are installed on the secondary side of power
transformers.
Is This Answer Correct ? | 20 Yes | 1 No |
Answer / rajendra
These capacitors are designed for protection of large
rotating machines such as motors & generators. At the time
of over voltage during electric storms produces surges to
electrical equipments connected to system. The voltage
stress between turns of multi turn coil sets a limitation
and surge voltage causes breakdown of turn to turn
insulation resulting in short circuited turns.
Is This Answer Correct ? | 5 Yes | 4 No |
what is the function of choke and starter in a tube light??
how to control the speed to switched reluctance motor
What is the difference between earthed and unearthed cable
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
What is difference between unity power factor wattmeter and upper power factor wattmeter? In short circuit test of transformer the wattmeter used is unity power factor type or upper power factor type wattmeter?
0 Answers Jindal Steel and Power,
why servomotor motor? where i apply for best output?
We have one 500KVA transformer. We have tested REF relay and commissioned. After one and half year, due to some ground fault in one of the DB circuit Transformer tripped by REF relay. What will be cause and remedy. Please advise?
generator means
What is the formula for calculating the Instantaneous Short Circuit & overcurrent for any breaker
Phase control and integral control are used for?
what is the difference between fault current ant short circuit current?
What is the suitable rating of MCB used for 1.5 Ton A.C & why?