Answer / thowsif_emerson_csm team
Calculation of Required Kvar:-
Initial P.f-PFi , Desired P.f-PFd and Real Power of Load in
KW...
KVAR=KW(tanAi-tanAd)
where,
Ai=Cosinverse(PFi) = Initial Power Factor Angle.
Ad=Cosinverse(PFd) = Final Power Factor Angle.
For Example:-
PFi=.85 & PFd=0.9 & Real Load=50 KW
For this required KVAR is 6.7 KVAR....
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / thowsif_emerson_csm team
Hi Pls Provide me the following Details:-
Input Load in KW....
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / sonam sherpa
P.F = M.D*(Tan(cos-1 x)-Tan(cos-1 y))
M.D - max. demand.
x- Actual power factor
y- Required power factor
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sonam sherpa
in above formual P.F- Capacitor rating in Kvar
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / akhilesh singh
please go through V.K.Mehta's book (power system)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sk rafiquil islam (kaithi,jamu
p=1.732*v*i*cos phaii so cos phai=p/(1.732*v*i) so,we can decrease of current we can developed pf
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ravi
Hi All,
Can u pls provide me the correct formula to calc.
P.f?????????????????
| Is This Answer Correct ? | 1 Yes | 3 No |
why impedance test in power cables?
Explain mechanical rotational system?
why the transformer ratings in kva or mva?
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
a.)Ammeter and Voltmeter read rms value or avg. value ? b.)What are symmetrical and Unsymmetrical faults?
What will happened. if we feed 3phase supplay to the stater with out insert the rotor. How much current will flow through the stater winnding?
In 400KV Switchyard, we have used Circuit Breaker With PIR, what is the significance of PIR & why they'r used?
What is the ratio of Booster transformer?
how many safety really of DG sets.
why middle phase should used for earth fault and other phases used for over current in overcurrent and earth fault relay?
i had aplied Hindustan Petroleum corporation limited for the post of maintenance technician -Electrical,i want model questions,if anybody have please send it or please advice?
what is the means of dedicate earthing?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)