Any one Give me formula for to increse the power factor,
0.8 to 0.95, How much the KVAr Required

Answers were Sorted based on User's Feedback



Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / thowsif_emerson_csm team

Calculation of Required Kvar:-

Initial P.f-PFi , Desired P.f-PFd and Real Power of Load in
KW...


KVAR=KW(tanAi-tanAd)

where,

Ai=Cosinverse(PFi) = Initial Power Factor Angle.

Ad=Cosinverse(PFd) = Final Power Factor Angle.

For Example:-

PFi=.85 & PFd=0.9 & Real Load=50 KW

For this required KVAR is 6.7 KVAR....

Is This Answer Correct ?    11 Yes 4 No

Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / thowsif_emerson_csm team

Hi Pls Provide me the following Details:-

Input Load in KW....

Is This Answer Correct ?    7 Yes 2 No

Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / sonam sherpa

P.F = M.D*(Tan(cos-1 x)-Tan(cos-1 y))

M.D - max. demand.
x- Actual power factor
y- Required power factor

Is This Answer Correct ?    4 Yes 0 No

Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / stanley

pls verify the whole questions. i just already give the
formula with examples.

Is This Answer Correct ?    2 Yes 0 No

Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / sonam sherpa

in above formual P.F- Capacitor rating in Kvar

Is This Answer Correct ?    2 Yes 0 No

Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / rupesh sharma

kvar= kw(tan phii- tan phir)

Is This Answer Correct ?    2 Yes 2 No

Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / akhilesh singh

please go through V.K.Mehta's book (power system)

Is This Answer Correct ?    0 Yes 0 No

Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / sk rafiquil islam (kaithi,jamu

p=1.732*v*i*cos phaii so cos phai=p/(1.732*v*i) so,we can decrease of current we can developed pf

Is This Answer Correct ?    0 Yes 1 No

Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required..

Answer / ravi

Hi All,

Can u pls provide me the correct formula to calc.
P.f?????????????????

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rating capacitor used, please give me Calculation. What is effact of consumer & suplier if pf is lagging or leading with on effect machines/ TF/GE etc.

6 Answers   L&T,


Difference between rating factor of cable and derating factor of cable?

0 Answers  


When electric field is parallel to the plane of incidence, the electromagnetic wave is said to be a.Linearly polarized b.circularly polarized c. Elliptically polarized d. Hyperbolically polarized

1 Answers  


why CT output is always raetd 5.regardsof primery curre.

3 Answers   ABB, BARC,


which Machine u will prefer to use at place where Flammable gases are coming out & why ??

6 Answers   NTPC,






In a synchronous motor armature current flows due to revolving flux which in turn rotates the load,but in no load condition armature current is zero hence thr is no revolving flux then how motor rotates?

9 Answers  


what is single phase motor?

5 Answers  


What is the difference between Earthing and Neutral?

13 Answers  


why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is function. i am going to instal a 5oo kva tranformer & 380 kva DG set what should the earthing value

8 Answers   Altrion Technologies,


1.what is the difference between ct and cvt? 2.what is the difference between pt and cvt? 3.what is the difference between relays and circuit breakers?

0 Answers  


what is the meaning of ceiling voltage in Generator exciter?

1 Answers  


How to calculate earth wire load by formula

0 Answers   Caparo,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)