Answer / thowsif_emerson_csm team
Calculation of Required Kvar:-
Initial P.f-PFi , Desired P.f-PFd and Real Power of Load in
KW...
KVAR=KW(tanAi-tanAd)
where,
Ai=Cosinverse(PFi) = Initial Power Factor Angle.
Ad=Cosinverse(PFd) = Final Power Factor Angle.
For Example:-
PFi=.85 & PFd=0.9 & Real Load=50 KW
For this required KVAR is 6.7 KVAR....
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / thowsif_emerson_csm team
Hi Pls Provide me the following Details:-
Input Load in KW....
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / sonam sherpa
P.F = M.D*(Tan(cos-1 x)-Tan(cos-1 y))
M.D - max. demand.
x- Actual power factor
y- Required power factor
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sonam sherpa
in above formual P.F- Capacitor rating in Kvar
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / akhilesh singh
please go through V.K.Mehta's book (power system)
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sk rafiquil islam (kaithi,jamu
p=1.732*v*i*cos phaii so cos phai=p/(1.732*v*i) so,we can decrease of current we can developed pf
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ravi
Hi All,
Can u pls provide me the correct formula to calc.
P.f?????????????????
Is This Answer Correct ? | 1 Yes | 3 No |
If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rating capacitor used, please give me Calculation. What is effact of consumer & suplier if pf is lagging or leading with on effect machines/ TF/GE etc.
Difference between rating factor of cable and derating factor of cable?
When electric field is parallel to the plane of incidence, the electromagnetic wave is said to be a.Linearly polarized b.circularly polarized c. Elliptically polarized d. Hyperbolically polarized
why CT output is always raetd 5.regardsof primery curre.
which Machine u will prefer to use at place where Flammable gases are coming out & why ??
In a synchronous motor armature current flows due to revolving flux which in turn rotates the load,but in no load condition armature current is zero hence thr is no revolving flux then how motor rotates?
what is single phase motor?
What is the difference between Earthing and Neutral?
why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is function. i am going to instal a 5oo kva tranformer & 380 kva DG set what should the earthing value
8 Answers Altrion Technologies,
1.what is the difference between ct and cvt? 2.what is the difference between pt and cvt? 3.what is the difference between relays and circuit breakers?
what is the meaning of ceiling voltage in Generator exciter?
How to calculate earth wire load by formula